Does anyone know how to load the "old" countervalue again in the actual coutervalue when an installation powers down, and up again?

I have programmed this but it does'nt work, programming error I think!
When a travel has been done and the counter is 500 mm.
When suddenly the power turns down and S7 starts up again it shows
the actual value is 0 mm (shown on a TP170A) but this must be the 500 mm instead

greatings Daevy
 
hello!
The counter does not have any memory when power is down.
Move the actual value to the loadvalue (or some memory place) and trigger the value when the plc starts up..
 
How are you getting this count value? Can you use an absolute encoder to retain the value at all times. Otherwise you have to do as already suggested.

cheers
 
Can the device that is being positioned move after power down (because of the inertia) ?
And, if this is the case, will it be a problem for the application if the position is wrong by a magnitude similar to the movement after powerdown ?
If so, then the only solution is to reset the encoder by moving it to the home position when a power-up is detected.
 
Ok, thanks folks.

I seem to have solved the problem by placing the old value in a DB-word and reload it in OB100 into the counter again.
Would there be people also have problems with it, I'can mail them an example program.

Thanks for the replies, but 3 hours of surching for a solution did it.
 

Similar Topics

I am replacing a 1756-OB16E 16 point 10-31 V DC card with the above card in a 16 slot Rack with a 1756-L71 control Logix 5570 controller. The...
Replies
0
Views
551
Hi, I've bought this PLC + HMI from Aliexpress, the one on the right that uses SSRs. and want to connect a 24V/0.2A DC fan to the output. My...
Replies
32
Views
7,097
Hi Everyone, Is it Possible to downgrade to Program from version 32 to 24version..? Because I have 24 version and the program which I am going to...
Replies
3
Views
1,074
Please laugh… but can I take 24volts from an IO module and wire it straight into its own input card to simulate an input….?
Replies
5
Views
1,262
Hello, There was a mix up in information on some redeployed equipment and two of the micro 1400's that came in were hooked to 120v when they...
Replies
9
Views
1,957
Back
Top Bottom