VersaMax NO contact using RS232, RS485, URGENT!!!

pavel47

Member
Join Date
Jul 2005
Location
Lausanne
Posts
20
Dear all

I have a problem trying to download my small example to VersaMax.

I tried both ports - Port1 (RS232) and Port2 (RS485).
Last one - with RS232-RS485 converter.

The software I use - Cimplicity Machine Edition v.4.0.
When I run download, it opens box "Connecting...", wait 2-3 min
and then gives the error of timeout.

I will be gratefull for any help.

Thanks in advance.

Pavel
 
I am assuming you have the same baud rate etc. and protocol set for the software and the PLC.

When I have encountered this in the past it was due to another program not releasing the comm port. In my case it was RSLinx. I had to shut it down, disable it from running automatically, and re-boot my laptop. Then I could connect no problem.

Check your PC's control panel and look at the status of the comm ports.
 
Thank you Tom

The problem is resolved.
I changed PLC and it works.
Former PLC was new (in sense it was never used).
Strange...

Former PLC showed faults at Port1 and Port2 LEDs.
 
I am using Cimplicity 7.5 with GE versamax PLC.There is RS 232 to RS 485 converter between PLC & scada.yesterday everything is running condition.when we restart the PC the communication is not done.on hmi the old values are showing & but in alarm bar the currently alarms are indicated.when I stop the scada & run again the following services are failed.
1)DA_RP_Failed
2)DA_RC_Failed
3)PRT_DC_Failed
4)PRT_DS_Failed
5)TRK_RP_Failed
6)PRT_CNT_Failed

can you help me please i am in big trouble on site now?
 
You should start a new thread, this does not relate to the OP from 2003.
I am using Cimplicity 7.5 with GE versamax PLC.There is RS 232 to RS 485 converter between PLC & scada.yesterday everything is running condition.when we restart the PC the communication is not done.on hmi the old values are showing & but in alarm bar the currently alarms are indicated.when I stop the scada & run again the following services are failed.
1)DA_RP_Failed
2)DA_RC_Failed
3)PRT_DC_Failed
4)PRT_DS_Failed
5)TRK_RP_Failed
6)PRT_CNT_Failed

can you help me please i am in big trouble on site now?
See my response in your other post of the same information.
http://www.plctalk.net/qanda/showpost.php?p=537224&postcount=9
 
Last edited:

Similar Topics

I have one GE Fanuc IC200PNS002-AC Versamax Network Interface Module and the fault red light is blinking and i have checked in manual it is...
Replies
9
Views
215
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
Replies
0
Views
132
I do have a problem with a GE Versamax micro PLC. By going online (on Port 1) the "OK led" goes down. Power led stays On Port 2 no reaction at...
Replies
4
Views
389
Hi, I am trying to set the IP address on the IC200UEM001 Ethernet Option Module. I am following the procedure in the manual for setting a...
Replies
1
Views
429
I have a new computer and it doesn't have an ethernet port. I am trying to connect to the Versamax Micro Plus with a type c to ethernet adapter...
Replies
7
Views
1,249
Back
Top Bottom