1769-hsc Reset

JamesWSY

Member
Join Date
Jul 2005
Location
Jakarta
Posts
81
I used 1769-HSC, CompactLogix processor 1769-L32E with incremental encoder to measure sheet length. I need help hot to reset the current count value (Local:1:I.Ctr0CurrentCount)to zero? Any idea? or sample RSLogix 5K?
Thank you for help.
James
 
If you have the hsc counting properly, you would use the following.
My HSC was in slot 13.

I would latch the reset on rung 15 and then reset it on rung 10 once itw as latched.

Rung 10 (XIC) Local:13:O.Ctr0SoftPreset OTU Local:13:O.Ctr0SoftPreset

Rung 15 Conditions and then (OTL) Local:13:O.Ctr0SoftPreset
 