rdrast
Lifetime Supporting Member
Gentle People.. Imagine...
You have a Very Long Pipe (oh, 800 feet), of relatively large diameter (say 6 inches ID) following what is basically a pure catenary....
Now, imagine you are going to charge that pipe with steam... up to oh, 400 PSI live steam.
Now, pretend you are going to back that steam up with some high pressure intert gas (at the top of the tube)
Now, pretend that you also have high-pressure water being injected into that pipe at the very bottom of it....
Now, pretend you want to control the actual level of the water in the pipe (which is on the catenary) *this pre-supposes you can actually MEASURE the water level* For water, we have pumps that can develop 650 to 800 PSI.
Now, pretend that there is a high-pressure seal on the other (top) end of the catenary... which in all cases must always be exactly 50 PSI higher then the steam pressure in the tube...
Now, pretend that the high pressure water pumps can develop 600 to 800 PSI, and must have a bypass system to keep the absolute output pressure (delivered to the tube) at 50 to 75 PSI over the steam pressure, but need to have a controllable bypass valve to dump the excess water back to the cooling towers....
Now, pretend that there are valves, near the steam/water interface in the tube that bleed off water to keep it at a certain temperature, but there MUST be actual WATER (NOT steam) flow...
How does one create a PID/PI/P/Anything system that can properly regulate the WATER LEVEL (And, for bonus points, how does one accuratly measure water level) in that kind of system?
Primary Setpoint is Steam Pressure.
Secondary Setpoint is (Top-Of-Tube-equizing pressure, 6 feet of 4 inch ID tube)
Secondary Setpoint is (Badly Sensed Water level In (6 inch Tube)
Tertiary Setpoint is (Water Pressure Delivered by high pressure pumps) (ed: does anyone else feel that 'pressure' should only have one 's'?)
The primary control, is on Steam pressure, however, the entire process will fail if the 1st secondary setpoint fails, or the tertiary setpoint fails.
The water level is critical. Steam PSI is the basis for everything... Top PSI is dependent on steam, but doesn't bleed off well. Water level is dependent on Water Pumps PSI > Steam PSI (to a point).
I see 4, interactive PID loops... Steam being the 'master control' of all the others. How would you make them all respond in a predictable, non-oscillatory fashion?
You have a Very Long Pipe (oh, 800 feet), of relatively large diameter (say 6 inches ID) following what is basically a pure catenary....
Now, imagine you are going to charge that pipe with steam... up to oh, 400 PSI live steam.
Now, pretend you are going to back that steam up with some high pressure intert gas (at the top of the tube)
Now, pretend that you also have high-pressure water being injected into that pipe at the very bottom of it....
Now, pretend you want to control the actual level of the water in the pipe (which is on the catenary) *this pre-supposes you can actually MEASURE the water level* For water, we have pumps that can develop 650 to 800 PSI.
Now, pretend that there is a high-pressure seal on the other (top) end of the catenary... which in all cases must always be exactly 50 PSI higher then the steam pressure in the tube...
Now, pretend that the high pressure water pumps can develop 600 to 800 PSI, and must have a bypass system to keep the absolute output pressure (delivered to the tube) at 50 to 75 PSI over the steam pressure, but need to have a controllable bypass valve to dump the excess water back to the cooling towers....
Now, pretend that there are valves, near the steam/water interface in the tube that bleed off water to keep it at a certain temperature, but there MUST be actual WATER (NOT steam) flow...
How does one create a PID/PI/P/Anything system that can properly regulate the WATER LEVEL (And, for bonus points, how does one accuratly measure water level) in that kind of system?
Primary Setpoint is Steam Pressure.
Secondary Setpoint is (Top-Of-Tube-equizing pressure, 6 feet of 4 inch ID tube)
Secondary Setpoint is (Badly Sensed Water level In (6 inch Tube)
Tertiary Setpoint is (Water Pressure Delivered by high pressure pumps) (ed: does anyone else feel that 'pressure' should only have one 's'?)
The primary control, is on Steam pressure, however, the entire process will fail if the 1st secondary setpoint fails, or the tertiary setpoint fails.
The water level is critical. Steam PSI is the basis for everything... Top PSI is dependent on steam, but doesn't bleed off well. Water level is dependent on Water Pumps PSI > Steam PSI (to a point).
I see 4, interactive PID loops... Steam being the 'master control' of all the others. How would you make them all respond in a predictable, non-oscillatory fashion?