Hi all

I have a Armour Point 4-20mA input module with a HART compatible transmitter on it. I cannot for the life of me get the HART to talk to my HART calibratitor (just doesnt see it)
I have the 150ohm resister between the output of the device (Joined in the cable near the plug into the input module) between the input devices output and the armour point plugs -

Any ideas anyone?????
 
" Hart " calibrators usually required 250ohms load. make sure you are connected across both 150ohm resistor and the input module. Which still might not be enough, I believe these modules have fairly low input resistance.
 
150 would be a typo

i meant 250 ohm :D

Im thinking its something to do with the armour point module, so I'm to try it using a I/P as the load instead
 
all seems to be good when not using the armour point as the input device....

must be something going on with that....
 

Similar Topics

Greetings, So this seems like it should be pretty simple, but I'm guessing there's something basic that I'm missing, and am hoping you guys...
Replies
14
Views
5,340
Hello, I have a module that gives a 4-20mA signal without HART interface. The customer uses HART and wants to be able to get both the 4-20mA...
Replies
10
Views
3,668
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
Replies
5
Views
274
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
Replies
7
Views
275
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
Replies
10
Views
1,693
Back
Top Bottom