4-20mA > HART
MrQ
Feb 2005
236
Hello,
I have a module that gives a 4-20mA signal without HART interface. The customer uses HART and wants to be able to get both the 4-20mA signal and the value via HART to their DCS.
Any ideas for black boxes. I have found repeaters but the way I understand they need a HART interface in the transmitter side also.
for you to send the module information to your customer, your module must have a Hart interface.
Nonuke is correct. Hart performance is built into the transmitter. If the transmitter does not have HART, it never will, with the sole exception of Honeywell's ST700/800 pressure transmitters with swappable comm modules.
I'm no expert, but every HART interface I have seen includes a 4-20 mA loop input. The 4-20 mA loop is the circuit on which the HART protocol is superimposed; you simply can't have HART without having a 4-20 mA loop.
I think that MrQ is looking for some kind of 're-transmitter' that will take in 4-20 mA on one side, then re-transmit the 4-20 mA as well as a HART signal containing the 4-20 mA value as the Primary Variable.
That sort of device might exist, but I can't see a reason for one; if the analog signal is the only input, then the HART data can only serve to duplicate or confirm the existing signal.
I suppose in somebody's mind this might be a way to improve 'signal confidence' by sending the same data both as analog and digital.
I'm very skeptical that you're find what you're looking for.
Only a tiny fraction of the AI's are capable of stripping off the HART data, mostly DSC's, a few high end PLC's or PAC's, so the HART market for analog is a fraction of the HART market for configuration.
The market for a device that has already suffered a D/A-A/D conversion which then takes the analog value (with that error) and converts it to HART and retransmits it, is your client, and your client alone, as far as I know.
The market for HART is
- configuration via HART
- multiple variables, like a coriolis meter or multivariable DP flow meter
- diagnostic data available via HART
- HART multidrop, primarily for diagnostics
- the occasional guy who knows that some minor error is avoided by getting the HART value and not getting the error from the D/A-A/D conversions (1 in 100,000)
Good luck looking, but in 20 years of HART stuff, I've never heard the request before, nor seen a commercial device that does what you're looking for.
I am also sceptical and realize that this is odd....
Another solution would be an analog output module with 4-20mA output and HART. Preferably for CAN bus.
Ideas?
An analog output with HART for a PLC is available. Allen Bradley's ControlLogix has a HART AO card.
The vendors are going to have to have a PAC product or be a player in the process world.
Remember the PLC card is a HART master, talking or reading from a HART slave field device. I'm not sure that that fits with what you're asking for. Field devices are always HART slaves, polled or written to by the DCS/PAC/PLC master.
I'm not sure an AO card HART master will communicate successfully to another HART master AI card.
I can't help you on CAN, it's not a player in the process world.
Congratulations! Talk about finding a needle in haystack!
The -8 4-wire model looks like it will do the job.
Greetings, So this seems like it should be pretty simple, but I'm guessing there's something basic that I'm missing, and am hoping you guys...
5,346
Hi all I have a Armour Point 4-20mA input module with a HART compatible transmitter on it. I cannot for the life of me get the HART to talk to my...
2,196
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
291
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
285
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
1,706