I am looking to be able to programmatically detect a change to several ControlLogix/CompactLogix from a PC-based application. In the older PLC/SLC technologies, there was a program checksum in the processor status file which suited this purpose.

Does anyone know of an equivalent program checksum in the ControlLogix/CompactLogix platforms? Or does anyone have a suggestion for a different way to detect a program modification?

Thanks.
 
check this from conroller properties -> file


time1.JPG
 
Yeah, I saw that edit date. The thing that I really need to do is to put that date into some tags in the controller so that a PC-based application could monitor that date. If it changes, then I know that someone has changed the controls program.

In the PLC-5, I could move the checksum into a register (such as N100:0) by this instruction:

MOV S:57 N100:0

Then the PC-based application could monitor N100:0 and look for changes.

So, for the CompactLogix/ControlLogix, I looked at using GSV to try and get the edit date, but it looks like it is only a property of the offline file and is not available in the online controller. Does that make sense?

So, as before, any suggestions would be appreciated.
 

Similar Topics

Hello, Have anyone here use Ignition to connect to a Remote IO using MQTT, then use ControlLogix or CompactLogix to connect to Ignition using...
Replies
1
Views
439
Im new to Ethernet/IP so I expected some issues but I am not sure if what I am trying to do is even possible. I believe these 2 PLCs should be...
Replies
6
Views
1,755
Hello! I'm struggling communicating a L320ER PLC through MSG Instructions, specifically I'm struggling with communication paths, I tried...
Replies
5
Views
1,330
I've been looking at some of the upcoming jobs we're doing where I work, and I feel like the scale would justify a ControlLogix instead of the...
Replies
11
Views
4,606
Client's Customer has an L64 v20 with MCI56-MCM Modbus in 2 slots. Client has an 1769-L16ER-BB1B v20 that needs to communicate with the L64 via...
Replies
3
Views
2,286
Back
Top Bottom