fluoronator
Member
GFI Breakers come with the neutral wire wound into a coil. Does this coiling of the neutral wire affect the operation of the breaker or can the neutral wire be straightened out for neatness of the installation?
Good intention. I wonder how many electricians know this. I also wonder how many of them straighten the neutral out, anyway.fluoronator said:After searching I've found the answer... I'll share it here as a conclusion to this post.
The during a ground fault condition there is a load on the GFI's neutral for a short period of time, the time required for the GFI to operate and open the circuit. If the neutral wire is straight, the current on the neutral will rise rapidly until the GFI operates. By coiling the neutral, inductive reactance causes the current to rise more slowly, therefore resulting in a lower peak current before the GFI opens the circuit.
cntrlfrk said:Do they make 480VAC GFCI breakers? If they do, how high of Amperage do they go?
We have issues in this plant where a ground faulted motor will take out the whole switchgear, thus causing a complete plant outage. Sometimes the fault is on an office air conditioner and the entire plant will suffer 6 hrs downtime to recover.
I've used ground fault detection on switchgear, which usually results in a 'needle in a haystack' search for a bad motor. Is there a better way to narrow down where the fault is?
fluoronator said:After searching I've found the answer... I'll share it here as a conclusion to this post.
During a ground fault condition there is a load on the GFI's neutral for a short period of time, the time required for the GFI to operate and open the circuit. If the neutral wire is straight, the current on the neutral will rise rapidly until the GFI operates. By coiling the neutral, inductive reactance causes the current to rise more slowly, therefore resulting in a lower peak current before the GFI opens the circuit.
fluoronator said:Okay, I've done further reading on the internal workings of the GFI and am convinced that the above answer is at least partially hogwash, I applogize for posting it prematurally. The GIF's neutral always carries the load, not just in a ground fault condition. If inductive reactance on the neutral plays any part whatsoever, it is VERY trivial. It seems that uncoiling the wire is okay.
cntrlfrk said:Do they make 480VAC GFCI breakers? If they do, how high of Amperage do they go?
Jim Dungar said:This "reasoning" makes absolutely no sense at all.
I've used ground fault detection on switchgear, which usually results in a 'needle in a haystack' search for a bad motor. Is there a better way to narrow down where the fault is?