GFI Breakers

cntrlfrk said:
I've used ground fault detection on switchgear, which usually results in a 'needle in a haystack' search for a bad motor. Is there a better way to narrow down where the fault is?

For motors use an Earth Leakage Relay. This is different from a GFI.

http://library.abb.com/GLOBAL/SCOT/scot260.nsf/VerityDisplay/D8A3B255544D297985257099004A46E4/$File/CM-IWN-AC.pdf

You wire the relay into your starter control cicruit or into a shunt trip breaker. They have an adjustable trip point from 1K to 110K ohms.
 
cntrlfrk said:
Do they make 480VAC GFCI breakers? If they do, how high of Amperage do they go?

We have issues in this plant where a ground faulted motor will take out the whole switchgear, thus causing a complete plant outage. Sometimes the fault is on an office air conditioner and the entire plant will suffer 6 hrs downtime to recover.

I've used ground fault detection on switchgear, which usually results in a 'needle in a haystack' search for a bad motor. Is there a better way to narrow down where the fault is?

Yes they make 480V breakers with Ground Fault Protection. Just do not confuse GF protection which is measured in amps with that of GFCI (sometimes incorrectly called GFI) people protection which is 5mA or GFPE (used on heater circuits) equipment protection which is in 30mA. Note: there are other terms and trip levels across the pond.

If you have a branch circuit take out your main breake it is because nobody paid for an engineering study which would have told you which settings (or additional eqipment) are required for proper coordination.

The methods for chasing down faults depends depends on if your system is solidly grounded (the most common), ungrounded (not common), or resistance grounded (becoming less rare).
 

Similar Topics

Does anyone have any recommendations for Electronic Circuit Breakers with 0V Terminals built-in and Fieldbus (IO-LINK, MODBUS TCP, EtherNet/IP?)...
Replies
2
Views
208
Hello everyone, I'm having trouble selecting the right circuit breakers for the "line side" of my VFD. The common advice is to check the...
Replies
21
Views
1,450
I'm thinking about using either in an upcoming project and I was wondering if anyone here had any experience with either. What are your thoughts...
Replies
2
Views
1,329
I am struggling with finding anything to support this. I really do not want to use UL489 breakers for the load side since they are expensive...
Replies
10
Views
3,226
Hi all, It seems to me that breakers are invariably more convenient than fuses. Fuses are difficult to remove, and if they discharge then they...
Replies
7
Views
2,870
Back
Top Bottom