anybody ever had a problem with a micrologix 1000 flaking out? our excel baler keeps shutting down, sometimes once a week, sometimes 10 times a day, stop loop seems fine, everything seems fine. when we open the cabinet the inputs are on, no outputs. starts right back up. ever had one flake out or drop out of run mode and back in to run mode?
 
on a side note, one of the motor contactors was clicking real bad and then the outputs dropped out. but i was checking the coil and it was constant, so i replaced the contactor, see how it does.
 
Make sure you have surge supression on all inductive loads and make sure
your ML is grounded properly. Then check the ground again and again.
 
thanks mickey, i will have them check that. sorry for the late replay, i have been in the air, back at home now.
 

Similar Topics

"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
129
Hi all, We have a very old pit pump system running on Micrologix 1000. Now, whenever there is an alarm for high conductivity, we want that alarm...
Replies
5
Views
1,256
Looking at a Micrologix 1000 1761-L32AWA, I tried to connect using the 1761-CBL-PM02 through a Serial to USB converter (This setup was used...
Replies
2
Views
985
Hello All I am trying to convert a ML1000 program for use in a ML1400. I didn't create the original program & documentation is non existent...
Replies
14
Views
4,409
Hey Folks, I have a customer with an older machine that is controlled with a MicroLogix 1000. The machine just quit working. The power light is...
Replies
22
Views
10,562
Back
Top Bottom