Ok, now I will be serious.
My vote is for one controller per machine where possible.
With a name of Peter North I doubt the OP is actually someone in charge of designing controls for a factory but who knows these days. My guess is a student.
This is a classic debate. Should I have 1 controller that controls 10 things or 10 controllers that each control 1.
If you have one controller and it goes down all 10 things stop. If you have 10 controllers you are 10 times as likely that something will go wrong (not really but you get my point).
I'll give you an example of a machine that I have dealt with that I thought should have had one or two PLCs.
The machine is a pipe mill, about 600' long with several different sections. This machine had 10 controllers on it and was designed in 1999. Several OEM's were involved with building it which explains the mess. Here is what everything did.
- Main OEM decided to split machine up into three sections. Accumulator, mill, and cutoff (3 SLC 5/04,s DH+)
- Entry OEM had their own 5/04 but where apparently too stupid to figure out a simple linear analog brake pressure controller for the mandrel brake and bought a DL-something and little HMI to do that.
- Welder had another 5/04
- 3 seam annealers each ahd their own 5/03
- Drive guy decided he needed an Automax controller for the drives (Reliance Flex Pak 3000).
- HMI guy decided he liked wonderware so main HMI was Intouch, the rest were panelviews.
- Motion control was necessary on the cutoff so an Indramat controller and a SOT (HMI) was installed there.
- Hydraulic control was necessary also on the cutoff so 2 rexroth HNC's were installed.
What a nightmare!. All of the PLC duties could have been handled easily by 1 5/04.
At the time the drive stuff was reasonable. Hey why not install the same system that you have been installing for the last decade even though it is about to be obsolete. Since the Reliance DCS won't talk DH+ lets install a third party protocol converter so it can talk to the PLC's, brilliant!
The HNC's had a bad habit of frying the 24V valve outputs if they got got shorted (approx 3K a pop), not to mention other problems, So I pushed for a Delta RMC. They were smart enough to go with a RMC after I left but too dumb to let one controller control both axis. So they bought two RMC's and networked them both with profibus (plant manager figured it was redundancy)
My point is that a machine (system) should be made as simple as possible and still do the job. If you have a million I/O points buy a fancy DCS, most of us don't.