Lancie1 said:The only "special technique" is to wire the incoming line to the TOP of the breaker, and the outgoing LOAD to the bottom. I know of cases where electricians have been electrocuted when the breaker was wired backwards.
He thought he WAS testing it. In this case the test is what killed him. This was the incident at the XXXXXXX XXXXXXXXXX Plant in Cherokee, Alabama. The floor was covered with damp (conductive material), the high voltage probe was dirty and untested, the breaker enclosure was poorly grounded, and the electrican was not wearing any protective equipment because he thought he was checking the dead end of the breaker to see if power was indeed off. He was an outside contractor called in to get the motor going. Later it was found that the plant electricians had wired the high-voltage line to the bottom of the breaker because the cables were cut too short to reach the top.That is why you should ALWAYS test it before you touch it.
abdou said:Genrally speaking, I normally try to protect transformers on both sides: primary and secondary , and using a three pole breaker for a single phase depends on the voltage I'm using:
- If a single phase lets say has a Neutral (120V, 277V), I don't need to protect the neutral, I only protect the phase.
- If a single phase is reffered to as (dual phase) (208, 240, or in this case 480V), Then you should use a " dual pole breaker" to protect both phases. But since a three pole breaker is handy, I would use it and i would double protect one of the phases( in and out to the third pole) as long you keep it Standard: your line/top and load/bottom,
- I will make sure that my breakers are sized accordingly to my demand.
fav quote: The reason is Abstract, but the reaction is clear!!!!
Bolt said:Are you talking about a breaker that's hard wired on both ends (vs snapping/screwing into a buss bar)?
Yes, "that's what I m talking about" If it was a breaker used by itself not from a "panel of breakers".
Yes, the NEC provides the minimum guidelines. If you do go against the "conventional method" or the "normal way", or the "what is usually expected", you had better have an excuse that is good enough to sacrifice some person's life.The NEC 110.3(B) allows breakers (actually it is the UL standards that do) to be wired "backwards" unless the brealer is specifically marked with LINE and LOAD designations.
Lancie1 said:Yes, the NEC provides the minimum guidelines. If you do go against the "conventional method" or the "normal way", or the "what is usually expected", you had better have an excuse that is good enough to sacrifice some person's life.
Before you run your test to check for safe conditions, make sure you know the actual situation and double check that your test can not endanger your life.