1756-OA16 output fusing/breaker recommendations...
Russ
Jun 2002
Ohio.. Go Bucks!!!!
261
The cards have two internal 3.15A fuses, one for each group, and a 0.5A max current loading per point @ 60°C (140°F).
They also have a 5A surge for 43mS per point, repeatable every 2 seconds.
These outputs will be pulling in relays, and turning on an indicator light, so there should be minimal surging.
I'm interested in protecting the outputs. My first thought is to stick with a 500mA breaker/fuse and call it a day. But with the surge rating, would a 1A breaker/fuse work just as well, or could the 1A breakers/fuses put the outputs at risk for potential failure?
About a year ago I lost a Compactlogix output card because one of the channels pulled close to 1A over a long period of time. When plant personnel cycled power on the cabinet, the beacon light turned on resulting in a failed point; and the card was toast.
I'd rather not repeat that again, if at all possible.
I've spoken with my local Allen Bradley distributer, who referred me to Rockwell Tech Support. The Tech Support Agent I spoke to likely won't be able to get back to me until next week (he didn't know the answer, and dropped the question into group chat).
It would be great to have an answer, or at least an understanding of what questions need to be asked, by Monday.
I don't see how fuses nor circuit breakers would remedy that situation. An interposing relay for the oversized load(s) would though.
Hi~ This is 1756-OA16 simply schematic. And I have two questions. Hope you can explain for me by this diagram. Thanks!! Q1:when no output...
5,044
Hi there, I'm using an AC output module (OA16) and I noticed the FuseBlown input word in my controller tags (Local:13:I.FuseBlown) and I don't...
2,016
When wiring this card and using 120 VAC dont you have to provide 120V power to the card and supply a neutral as well?
1,708
I need any information where can I download firmware V3.2 for output card 1756-OA16/A. This is very unique card, has different hardware and...
2,629
On an out of town startup and through the night one of 1756-OA16 cards blew a fuse on a group of 8 outputs. Traced problem back to faulty Neutral...
17
16,364