1756-OA16 I.FuseBlown Word
aj2004
Sep 2015
burnaby
Hi there,
I'm using an AC output module (OA16) and I noticed the FuseBlown input word in my controller tags (Local:13:I.FuseBlown) and I don't quite understand what the bits represent.
I am familiar with the I.FuseBlown status word for a 1756-OB16E output module, for example. Each of the first 16 bits represents an electronic fuse for the corresponding output has "blown".
The user manual for digital I/O says that, for the OA16, each of the 2 groups of outputs (0-7 & 8-15) is fused internally. However, I can't figure out how the actual FuseBlown bits work for this module.
Does I.FuseBlown.0 = Group 0 (outputs 0-7), or Output 0?
If the Group 0 fuse blows, are the FuseBlown bits 0-7 set to 1s?
Or is FuseBlown.0 for Group 0, and FuseBlown.1 for Group 1?
Thanks!
aj2004 said:
Does I.FuseBlown.0 = Group 0 (outputs 0-7), or Output 0? - No
If the Group 0 fuse blows, are the FuseBlown bits 0-7 set to 1s? - Yes
Or is FuseBlown.0 for Group 0, and FuseBlown.1 for Group 1? - No
For the 1756-OA16 Output Module there are two internal fuses on the PCB for the two Groups of Output points -
Fuse in middle of PCB = Group 0 - Outputs 0-7
Fuse at bottom of PCB = Group 1 - Outputs 8-15
I.FuseBlown.0-.31 Indication...
Note: FuseBlown Input Word is a 32-bit DINT
When a fuse is blown the corresponding Group bits in the FuseBlown Input Word will be set to 1 as follows -
Group 0 = bits 0 through 7
Group 1 = bits 8 through 15
Bits 16 through 31 do nothing
Binary Representation...
Group 0 Fuse Blown = [31-0] 2#0000_0000_0000_0000_0000_0000_1111_1111
Group 1 Fuse Blown = [31-0] 2#0000_0000_0000_0000_1111_1111_0000_0000
The Blown Fuse LED indicator will illuminate if either Group fuse blows, but there must be a load on at least one Group Output for it to be detected, else the LED will not illuminate.
Regards,
George
Thanks for your help!
For anyone else that finds this thread, here is the logic I used to monitor these bits:
Lower Bits 0-7:
BTD (Bit Field Distribute)
Source: Local:13:I.FuseBlown
Source Bit: 0
Dest: Local_Slot13_FuseSts_Lower (DINT)
Dest Bit: 0
Length: 8
In series with a NEQ 0 to turn on a "FuseBlown_Lower" OTE
Upper Bits 8-15:
Source Bit: 8
Dest: Local_Slot13_FuseSts_Upper (DINT)
Dest Bit: 0
Length: 8
In series with a NEQ 0 to turn on a "FuseBlown_Upper" OTE
This could probably be done with AND instructions using a bitmask, but the existing logic in this routine uses BTDs, so I stuck with the same format.
The cards have two internal 3.15A fuses, one for each group, and a 0.5A max current loading per point @ 60°C (140°F). They also have a 5A surge...
1,068
When wiring this card and using 120 VAC dont you have to provide 120V power to the card and supply a neutral as well?
1,712
I need any information where can I download firmware V3.2 for output card 1756-OA16/A. This is very unique card, has different hardware and...
2,631
On an out of town startup and through the night one of 1756-OA16 cards blew a fuse on a group of 8 outputs. Traced problem back to faulty Neutral...
17
16,369
Hi~ This is 1756-OA16 simply schematic. And I have two questions. Hope you can explain for me by this diagram. Thanks!! Q1:when no output...
5,045