The Drivers for the 1747-UIC were lost therefore the interface could not be used and had to have the Drivers re-installed.
Couple up the USB-DH485 (1747-UIC) between the PLC and PC before powering up the PC.
The PC should detect the USB hardware and load the Drivers.
Click on Start > Control Panel > System > Hardware > Device Manager then expand Ports (COM & LPT) to find which port you have connected to. Note it, then exit back to the desk top.
Execute RSLinx. Uncheck the Autobrowse box near the top left corner. Click on Communications and Configure Drivers. You should see under Configured Devices the following: AB_DF1-1,DH485…. If this shows Port Conflict then click on Stop. Re-highlight this line then click on Configure. Enter the com port you are connected to in Comm Port:.
Ensure
You have selected the correct com port.
Device: 1770-KF3/1747-KE
Baud: 19200
Station Number: 00
Parity: None
Error Checking: CRC
Stop Bits: 1
Protocol: Full Duplex
DO NOT auto-configure. Click on OK.
Highlight the new data under Configured Devices and click on Start to which Running will be displayed in place of stopped. Click on Close to go back to the Browsing screen. Check the Autobrowse box to enable node browsing. Your PLC node should appear, if not exit RSLinx then re-enter RSLinx.