First, yes I have done a search :D
The standard answers seem to be use PROFIBUS.

However, If possible, I would like to setup communications over Ethernet. I have done it in the past via PROFIBUS with the ControlLogix as a slave.

Any hardware recommendations and / or sample code?

Thanks

Mike
 
Simatic: S7-300 or S7-400?
S7-3?? + CP 343-1 Lean 6GK7 343-1CX00-0XE0. UDT supported.
S7-3??-PN/DP no UDT supported, so cant use multi- or broadcast connections.
Use AG_SEND and AG_RECV from Example Library SIMATIC_NET_CP
 
It will be with a S7-300.
What interface at the ControlLogix side (ENBT / ENET / EWEB)?

Do you have sample code?

Thanks
 
JRW said:

Looking at that gateway device, it solves the issue of S7-300 Ethernet communicating to Contrologix and Contrologix communicating to the S7-300 via ethernet.

But, the data transfers are limited to INT (16 bits ) only. If I had a choice to transfer blocks of data back and forth 16 bits at a time, I would go with Profibus.
 
Mike_RH said:
What interface at the ControlLogix side (ENBT / ENET / EWEB)?..Thanks
I don't know CL, so if there is "Socket" (IP and Port) Connection, it sounds good. Block send and receive needed as well as in Simatic AG_SEND/AG_RESV.
I have Simatic examples:
- Interlocks and messages between PLCs (Interval), Multicast/UDP.
- Message only (COS), Socket/TCP.
Please send your email address.
 
Last edited:
Yes, a direct ethernet connection is possible with sockets. I even think there are someone on this forum that has accomplished it - or was that on mrplc.com, or was it on sps-forum.de ?
Anyway, it is only possible with the EWEB module, not the ENBT.
 
Thanks for the replies.
I think I will go scrounge up an EWEB module and see if I can get this to work.
 

Similar Topics

Hi All, Looking to get some direction on how to get data from a piece of equipment that has RS-232 communication (1-way) to a 1756-L73...
Replies
7
Views
356
Hi Guys, I'm trying to integrate Pilz Ethernet IP Module to ControlLogix. I added Pilz module as a Generic Ethernet module and I'm able to...
Replies
2
Views
527
Hello all, I was wondering if you clever people could help me, please. In the past I have used a standalone L33ER CompactLogix PLC with the...
Replies
5
Views
1,564
PLC is ControlLogix 1756-L73 CPU with firmware 28 In the PLC the value for A60[110] is "AT", Style ASCII, Data Type INT. In KEPServerEX I tried...
Replies
4
Views
1,596
I am building a ControLogix network with about 70 nodes. I was going to use a 1756-EN2T. Until I noticed that the 1756-EN4TR has way more...
Replies
3
Views
2,113
Back
Top Bottom