Sorry for diverting your thread, zif2, I'll keep this short.
Here's the scoop with the SCANport/DeviceNet adapters; this goes for the 1203-GU6 and the 2100-GK61.
The DeviceNet node number and data rate can be changed in two different ways: through the DeviceNet Object (Class 0x03) or through the Parameter Object (0x0F).
The DeviceNet Object is accessed with handheld configurators or the DeviceNet Node Commissioning utility. If you double-click on the node number of a device in the graphical view of RSNetworx, that brings up the Node Commissioning utility. Those changes take place immediately.
The Parameter Object is what you're accessing using the traditional Parameter Editor in RSNetworx for DeviceNet software. The "DN Node Address" and "DN Data Rate" parameters (Parameters 326 and 327 on the drive I have right here) only take effect when power is cycled.
So what usually happens is that a technician browses a DeviceNet with RSNetworx software, but he has a blank project file. When the drive shows up on a network browse, he goes online and answers "Download" when the software prompts him to upload or download in order to go online.
Presto ! He's just loaded the default data rate and node number parameters into the 1203-GU6 (because he hit *download* from a default project file). They don't take effect until power is cycled, which might be days or weeks later.
Other scenarios I've seen include one technician (the new guy) whose standard M.O. was to hit the "default values" button in RSNetworx, then to set up the parameters he knew he had to change (but omitted the node and data rate). When the power was cycled.... ta-da, all the drives he set up were at Node 63, 125 KB/s.
There's nothing to be done except to make sure folks with access to the network have at least a little training in RSNetworx procedures.
"It's not voodoo, it's just DeviceNet !"