Grounding operator panels

Plc_User

Member
Join Date
Dec 2005
Location
Belgium
Posts
317
What could be the bad effect if touch panels are not connected to ground (only + and 0 voltage are attached). I can believe that the influence is poor for a small configuration, but on a bus system with a lot of connected slaves?

Thanks
 
If you are using RS-232 for your communications, it could be fatal to the PLC and the HMI since RS-232 is a ground referenced signal.

In this case, the panel will try to derive it's ground from the PLC through the communications wire. If the panel ground reference is not close to the PLC ground reference, it can and will cause the com ports to die from too much impedence.

Panel manufacturers put ground points on the HMI's because they are needed to make sure that communications lines are balanced and so that any noise has a dissipation path.
 
nonuke said:
Isn´t the 0V of the PS connected to Ground???

No, there is no reason or rule (in the US) that mandates the negative voltage (or 0 volts) be grounded. I have plenty of machines that float the 24 VDC with no problems at all.
 
I always ground all my 0V and Never had a problem.

This way all the control panels and Power Supplies in the network are ref. to the same point (ground).
 

Similar Topics

Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
Replies
5
Views
273
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
Replies
9
Views
435
Hi, Our customer has bought a machine a CNC wood cutting machine. It states that it need a seperate 16mm2 EMV"ground" in addition to our 5G16mm2...
Replies
2
Views
602
I have a Beckhoff PLC with many AI modules. Most devices are loop powered using the same +24 VDC power as the Beckhoff Bus Coupler and all is...
Replies
5
Views
668
I was once asked a question in a job interview. "Do you ground both ends of a shield?" I answered: "You only ground one end". Apparently that was...
Replies
12
Views
4,949
Back
Top Bottom