Hi:

I was seeing the manual of FT Alarms&Events and indicates that CompactLogix firmware version 16.20 and higher is compatible with FT Alarms.

I have a L32E CPU and upgraded the firmware to version 16.3 But in FTView send me a message "Connection to controller <RSlinx Shortcut Name> has been lost." in my Alarm and Event Summary (but I see the controller in the shorcut and the tags in my displays, in fact, I can start and stop motors from that processor), the message is only from the alarm server.

Anmy idea that I can do?Another firmware?

Thanks
 
I am using FTView SE with a client/server connection. The message appears in the Studio and in the client alarm summary.
 
From the built-in web page of the CompactLogix Ethernet port or using the Logix 5000 Task Monitor, measure how many CIP connections your controller is handling.

This is only a guess, but because FT Alarms & Events uses a separate CIP connection for the alarm subscription, your controller might have too many combined FactoryTalk and I/O connections on the communication port.
 

Similar Topics

So I have Factory Talk ME ver 12 and Studio 5000 ver 32. Hardware is a 2711P_T7C21D8S 7" Panelview Std connected to a CompactLogix L30ER. I am...
Replies
6
Views
2,291
Hi there, I am currently working on a project that involves interfacing PowerFlex525 drives with a CompactLogix PLC over Ethernet/IP One thing I...
Replies
9
Views
3,167
Is there a way to print alarms from either a CompactLogix or a PanelView Plus 1000 via ethernet? I would only need to print certain alarms at...
Replies
1
Views
2,852
Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
95
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
98
Back
Top Bottom