Hello everybody,


I need some advice.


I have the "pleasure" to make service on one old machine with Simatic CPU 315 (old one with battery) and with magic text display TD17.

This machine is working more then 10years with small problems only, but now everithing change :)

TD17 start to signal the system message: PLC address not exists...

So i first look inside the PLC if it has the correct address. It was OK.
Then I tried to check the connectors and the cables with new ones, but it was the same.
Then i tried to download new configuration to the panel. Nothing change.
So i tried to change address in PLC and in TP to some other. Still the same.
So finaly i take the cabel and connect it to differnt panel (there four of them) and everthing works. So the PLC and the cables are OK.

I suppose that TD17 comm. port is "dead". But maybe it is somthing different and somebody knows what to do :)


Please help me if you can :)
 

Similar Topics

HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
82
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
Replies
2
Views
166
Hi, I received this SIMATIC S7-300 training kit for maintenance. When I power it up, the PLC doesn't go to RUN mode and the STOP mode led is...
Replies
7
Views
301
I'm trying to build my Classic Step 7 programming skills this weekend. I get stuck on little things that are not covered in YouTube tutorials. I'm...
Replies
7
Views
316
I am utilizing both HMI and SCADA for my project. Both HMI and SCADA have identical tags. When I modify the tag value on HMI, it is reflected in...
Replies
2
Views
151
Back
Top Bottom