multiple 1785-enet

MajorFault

Member
Join Date
Nov 2007
Location
Louisiana
Posts
36
Can you run multiple 1785-ENET cards in a plc 5/40e?
I would like to have one for a scada system connection, and another to a pc based system that will give the PLC target setpoints for a motion system. That's two subnets.
Is that possible?
 
The 1785-ENET connects to the CPU using a 50-pin card-edge connector, rather than the 1771 backplane.

You cannot connect more than one to a PLC-5 controller.
 