You can use the same output number in several rungs with this PLC. However, it is not good practice. The last incidence of the output in the program will overwrite all other incidences.
It is not good practice!!
 
Generally its a case of "The last one wins" as the state of the output in the image table table at the end of the scan is then transferred to the output card.
If you go to youtube and search for Ron Beufort, his training videos explain this well.
Alternatively you can use a Set / Reset coil or Latch / Unlatch, this is also explained in the videos.

Hope this helps

LH
 
You can use the same output number in several rungs with this PLC. However, it is not good practice. The last incidence of the output in the program will overwrite all other incidences.
It is not good practice!!

Don't know if there are jump instructions in this PLC, but multiple use of the same coil is quite often used in sequencing programs with no ill effect and no 'bad practice' syndrome.

Also as above using latch and unlatch.
 
Hi
I agree with the jump instructions comment but in this case i would say good practice would be to use diffent internal marker coils, and then parallel these to the real output.
I have worked on a program using jumps for sequencing and would not recommend the method where the same coils are used over and over.........clever technique but a pita to faultfind
 
TriStation 1131 Developer's Guide, v4.6

While reading through this guide I came across this
"Enable Multiple Writes
The Enable Multiple Writes property specifies whether a tagname can be written to multiple
times from programs in the application. If this property is not selected and the tagname is
written to more than once, an error is displayed when the program is compiled.
The default is cleared, which means the tagname can only be written to once in an application."

During programming the Triconix PLC I noticed that If the Enable Multiple writes option was not selected the program gives an error if an output is written more then once. And if enabled I think double coil syndrome happens.
 

Similar Topics

Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
Replies
1
Views
124
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
Replies
18
Views
1,478
Hi, I am trying to get a machine started that was moved from one location to another. It has a Modicon 984-A131 PLC. I have Schneider Electric...
Replies
1
Views
1,034
Hello All. We have a 1756-17 slot chassis with analog ins and outs in the entire rack along with the EN2T card. Up until recently everything was...
Replies
1
Views
1,499
Hello, I have a drive allen bradley powerflex70 that works normal it shows that it has start and frequency variation but there is no output 0...
Replies
2
Views
2,123
Back
Top Bottom