Ok I need to figure out the safest way to wire is a wet area.

The box will be sealed but in a wet area the plc will be controlling a couple of small pumps that will be in water and some probes in water.

As it sits right now the power to the plc and i/o is comeing from a GFCI breaker.

As it sits now I feel it is safe.

Now I am adding a upc or I guess its called a back up battery to maintain power to one pump and the plc (one pump 3amp has to stay on). But doing this I will think would kind of bypass the GFCI So how do I do this safely?
 
if i understand correct
Put GFCI on UPS inverter output
other pump circuit would also be GFCI

Better yet if within HP range go with a battery direct supplied DC pump pump relay controlled by PLC
OR on loss of AC a dropout relay to start DC pump

Dan Bentler
 
if i understand correct
Put GFCI on UPS inverter output
other pump circuit would also be GFCI

Better yet if within HP range go with a battery direct supplied DC pump pump relay controlled by PLC
OR on loss of AC a dropout relay to start DC pump

Dan Bentler

I just got lost with that

But I think that you are saying to put a GFCI receptical on the output side of the ups right

as far as the dc pump they dont make one for this aplaction
 
several things to consider in hostile wet enviroments first is standoff mounting to allow washdown to flow behind the panel from washdown. Second is make sure all conduit is mounted from the bottom. You may also consider adding a thermostat and heater din rail mounted.
 
I will mount all wireing from the bottom The issuse I am more worried about is the pump being in water and couseing personel to get shocked if something happens
 
If the pump is rated as submersible and is properly fused coupled with your GFI this shouldn't be a problem and is fairly common in waste water applications. Keep in mind the pump must be rated submersible
 

Similar Topics

Good Morning , I need to make a online change to a SLC 500 5/05 . Is it safe to turn the key from Run to Remote with causing the processor...
Replies
2
Views
1,887
Hi All How to remove USB device safely on a PC locked with Desklock? there is no taskbar) Using win2k Thnx
Replies
6
Views
2,559
We had an application were 5 drives were moving 8000lb at 72 ips. In case of fault when running at speed, what is responsible for safely and...
Replies
41
Views
13,411
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
Replies
9
Views
315
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
Replies
1
Views
98
Back
Top Bottom