Hello to all,

my name is nagaraj from Bangalore,

Actuall i have a RTD PT100 2 wire type and it is fixed 30 meter away from the PLC panel,So which cable i shall laid between PLC RTD module to the instrument?
Give me the specification of the cable and distrubutor in Mumbai (india)if you can...
Many thanks in advance..

Regards,
Naag.
 
You should use a 3 conductor twisted with an overall shield commonly known as Instrumentation Triad.
Belden is a brand I am familiar with
 