Panel view 600 and slc 5/03

urvinder_pal

Member
Join Date
Mar 2009
Location
surrey
Posts
38
This being thE first time i am trying to work with a panelview 600 AND SLC 5/03.I keep on getting the error no active nodes found. Can someone let me know what is missing that would establish a connection between the two. I am using 2711-NC13 CABLE.

IN THE PANELVIEW COMMUNICATION SETUP I HAVE

NODE ADDRESS 2
MAX NODE ADDRESS 31
BAUDRATE 19200

UNDER NETWORK NODES

NODE NAME slc

NODE ADDRESS 1

NODE TYPE SLC 5/03 - OS 302

IN RSLOGIX 500 UNDER CHANEL CONFIGURATION


UNDER GENERAL
CHANEL 1 DRIVER DH485

CHANEL 1 SYSYEM DRUVER DH 485
BAUD 19200
NODE ADDRESS 1(DECIMAL)


UNDER CHANEL 0 SYSTEM

DRIVER DF-1 FULL DUPLEX

BAUD 1200

PARITY NONE

SOURCE ID 9(DECIMAL)

ERROR CRC


DOES THIS BAUD RATE HAVE TO MATCH WITH SOMETHING

PL ADVICE.


THANKS TO ALL
 
Please tell us the complete catalog number of your Panelview.

Also which port on the SLC5/03 are you connecting the PV to?

Is there any other hardware involved with this connection?

From the cable you listed, it looks like you are connecting from the SLC5/03's serial port to the PV. If so then channel 0 on the SLC5/03 ( serial port/RS232)
will have to be configured for DH485. Same baud rate as the PV with a different node address.

But with answers to the above questions we will not have to guess.
 
Last edited:
panelview 600 and slc 500

Please tell us the complete catalog number of your Panelview.

Also which port on the SLC5/03 are you connecting the PV to?

Is there any other hardware involved with this connection?

From the cable you listed, it looks like you are connecting from the SLC5/03's serial port to the PV. If so then channel 0 on the SLC5/03 ( serial port/RS232)
will have to be configured for DH485. Same baud rate as the PV with a different node address.

But with answers to the above questions we will not have to guess.

panel view cat no: 2711-B6C5, SERIES B FRN 4.21

I AM USING SLC SERIAL PORT

THERE IS NO OTHER HARDWARE INVOLVED

THANKS
 
panel view cat no: 2711-B6C5, SERIES B FRN 4.21

I AM USING SLC SERIAL PORT

THERE IS NO OTHER HARDWARE INVOLVED

THANKS

Then with your 2711-NC13 cable and your SLC5/03' serial port configured for DH485, Baud rate the same as the PV, node address different then the PV you should be good to go.
 

Similar Topics

Hi Everyone, I am new to the site and to plc programing. Always been the guy trouble shooting around them. I have a Panelview 600 2711-b6c8...
Replies
6
Views
1,319
Hello everyone I have a PanelView Plus 600 that is acting up. To be able to go into our manual operations of the machine it runs, a small fluid...
Replies
18
Views
4,972
Dear expert /Group members Good day to your Does anyone have this problem? Problem explanation as below :- Thanks in advance
Replies
1
Views
1,047
Hello everyone, im new in Allen Bradley World, i alredy know how to use factory talk view and with manager i have alredy upload all runtime...
Replies
1
Views
1,701
Trying to connect an old panel view 600 to a control logic processor over device net I have devicenet connected but can't seem to address the...
Replies
7
Views
1,649
Back
Top Bottom