This being thE first time i am trying to work with a panelview 600 AND SLC 5/03.I keep on getting the error no active nodes found. Can someone let me know what is missing that would establish a connection between the two. I am using 2711-NC13 CABLE.
IN THE PANELVIEW COMMUNICATION SETUP I HAVE
NODE ADDRESS 2
MAX NODE ADDRESS 31
BAUDRATE 19200
UNDER NETWORK NODES
NODE NAME slc
NODE ADDRESS 1
NODE TYPE SLC 5/03 - OS 302
IN RSLOGIX 500 UNDER CHANEL CONFIGURATION
UNDER GENERAL
CHANEL 1 DRIVER DH485
CHANEL 1 SYSYEM DRUVER DH 485
BAUD 19200
NODE ADDRESS 1(DECIMAL)
UNDER CHANEL 0 SYSTEM
DRIVER DF-1 FULL DUPLEX
BAUD 1200
PARITY NONE
SOURCE ID 9(DECIMAL)
ERROR CRC
DOES THIS BAUD RATE HAVE TO MATCH WITH SOMETHING
PL ADVICE.
THANKS TO ALL
Please tell us the complete catalog number of your Panelview.
Also which port on the SLC5/03 are you connecting the PV to?
Is there any other hardware involved with this connection?
From the cable you listed, it looks like you are connecting from the SLC5/03's serial port to the PV. If so then channel 0 on the SLC5/03 ( serial port/RS232)
will have to be configured for DH485. Same baud rate as the PV with a different node address.
But with answers to the above questions we will not have to guess.
panelview 600 and slc 500
panel view cat no: 2711-B6C5, SERIES B FRN 4.21
I AM USING SLC SERIAL PORT
THERE IS NO OTHER HARDWARE INVOLVED
THANKS
THANKS
Then with your 2711-NC13 cable and your SLC5/03' serial port configured for DH485, Baud rate the same as the PV, node address different then the PV you should be good to go.
Hi Everyone, I am new to the site and to plc programing. Always been the guy trouble shooting around them. I have a Panelview 600 2711-b6c8...
1,330
Hello everyone I have a PanelView Plus 600 that is acting up. To be able to go into our manual operations of the machine it runs, a small fluid...
18
4,987
Dear expert /Group members Good day to your Does anyone have this problem? Problem explanation as below :- Thanks in advance
1,056
Hello everyone, im new in Allen Bradley World, i alredy know how to use factory talk view and with manager i have alredy upload all runtime...
1,728
Trying to connect an old panel view 600 to a control logic processor over device net I have devicenet connected but can't seem to address the...
1,663