simatic tp177 micro

stevefoes

Member
Join Date
Dec 2005
Location
christchurch
Posts
9
We have updated s5 to s7200 ,just downloading to the screen TP177 micro using win flex 2005. This will not communicate as the download for the screen from siemens site says it is looking for the older version software 2004 . Is there any fix around this or does the pannel have to be a TP177 "6" .
 
When i do not have the same OS on panel and Winccflex I use aplication in winccflex caled OSupdate which udates OS on panel.
I didnt use it on this panel but on biger panel this works fine.

select Project - Transfer - Osupdate
as described in manual

Updating the operating system using WinCC flexible
Requirements
• The HMI device is connected to a configuration computer.
• No project is open in WinCC flexible.
Procedure
Proceed as follows:
1. Switch off power to the HMI device.
2. Select the menu command "Project ▶ Transfer ▶ Communication Settings" in WinCC
flexible on the configuration computer.
This opens the "Communication Settings" dialog.
3. Select the HMI device type.
4. Set the connection parameters.
5. Close the dialog with "OK".
6. In WinCC flexible, select the menu command "Project ▶ Transfer ▶ Update operating
system".
7. In "Image path," select the folder which contains the HMI device image file, *.img.
The HMI device image files are available under "WinCC flexible Images" in the WinCC
flexible installation folder and on the corresponding WinCC flexible installation CD.
8. Select "Open".
In the output area, you are provided information on the version of the HMI device image
file after it is opened.
9. In WinCC flexible, select "Update OS" to run the operating system update.
Follow the instructions in WinCC flexible.
A status view opens to indicate progress.
Result
The system outputs and alarm when the operating system update is completed.
This operation has deleted the project data from the HMI device.
 

Similar Topics

Hello. How to protect access to some views : Hardware : Siemens SIMATIC TP 177micro Software : SIMATIC WinCC flexible Micro...
Replies
0
Views
3,618
Hi all. I am using a TP177 Micro and would like to know if there is anyway in which I can change the current active screen from the PLC. I am...
Replies
3
Views
5,093
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
81
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
Replies
2
Views
164
Hi, I received this SIMATIC S7-300 training kit for maintenance. When I power it up, the PLC doesn't go to RUN mode and the STOP mode led is...
Replies
7
Views
300
Back
Top Bottom