hello
I was wrong and I accidentally gave cancel while downloading a program and now fault led flashing
fail to connenct to slc with rslogix and rslinx with my rs232 cable
appears this message with rslogix:"no response from processor at selected path/node" and below "diagnosticstatus failed : 0x4"
how can I fix the problem?
many thanks
 
hello
I was wrong and I accidentally gave cancel while downloading a program and now fault led flashing
fail to connenct to slc with rslogix and rslinx with my rs232 cable
appears this message with rslogix:"no response from processor at selected path/node" and below "diagnosticstatus failed : 0x4"
how can I fix the problem?
many thanks

If the Fault LED is Flashing, you should still be able to connect to the PLC. Close your project in RSLogix500. Shutdown RSLinx and restart it again. Then open your RS-232 Drive and do an Autoconfigure. Hopefully, you should be able to re-establish communications. Once you have, you can open your project in RSLogix500, and Download it.

Stu....
 
I tried but it did not work.
I wrote a new program and tried to connect and nothing.
I reconfigured driver in rslinx and nothing
I stopped power for slc and nothing
no communication
is possible to delete everything without communication?
lader diagram is not important.
many thanks
 
thanhs for Answers and documentation!
i clear memory(i hope)but no works.
I found ab pic and victory,connected to the first time.
clear errors and now works.
this is good news. the bad news is that it does not work my rs232 cable. o_O
rslinx not found station and not configure driver df1.
any suggestions?
 
using the DF1 driver with RSLinx should auto configure.

Make sure no other program is using the port, usually COM1
Try using a null modem rather than straight through serial
Completely shutting down RSlinx and then restart
 
hello again
I tried to autoconfigure DF1 driver with RSLinx but no works.
says check cable o_O
ab pic driver communication with my plc but no communication between rsworks and plc.
i uninstall rslinx 2.57 cpr9 and install 2.43 cpr6 and now rsworks communocation with my plc.
i tried again df1 driver but same problem:"check cable".:cry:
 
obvious but when doing an auto configure you are making sure to select slc 5/03 before doing the auto configure
 
Are you using a USB adapter or do you have a serial connection at your pc?
Post a screen shot of your configuration in rslinx
 
Last edited:
oaie,

Post your .RSS file here ( zip it first) and someone can take a look at your SLC5/03's serial port configuration.
 
Does your serial port work at all? I've run into something in the field in which my serial port got "fried" some how and I had to buy one of those USE to serial converters and switch my COM port number.
 
According to your screenshot, you have a PLC-Ch0 selected. Your connecting to a SLC. You need to select that.
 

Similar Topics

Hello all! I have some machines that run an SLC 5/03 and occasionally a fault is generated. Recent Example: A power supply wasn't screwed in...
Replies
3
Views
421
hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
Replies
7
Views
3,015
Has anyone ever seen this fault or have any insight as to what it was. I found this on an SLC 505 after we had the main breaker off working in...
Replies
1
Views
1,412
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
Replies
9
Views
1,800
Hello! We have a drum rotation machine controlled by a AB SLC 500. The drum rotation inputs comes from a encoder into a 1746-HSCE. We are using 2...
Replies
0
Views
1,134
Back
Top Bottom