1756-IF8 Scaling

gjsangster

Member
Join Date
Nov 2010
Location
Edmonton
Posts
6
Hi I am new to this forum and new to RSLogix5000. I have programmed alot with RSlogix500 and have began working my way through my first project using 5000. Here is my problem there is no SCP function in 5000. I have 4 potentiometers as an inputs 0-10Vdc and 1 as 0- -10Vdc all wired to a 1756-IF8. I set up the Comm Format tab for Interger Data-Single Ended Mode and setup all the input ranges. Now the module is configured I thought I could go back and setup my scaling in the card. But it does not give me this option to setup engineering units. I have to scale these inputs to 0 - -8.2Vdc which are in turn outputed via 1756-OF8. I have included a screen shot of the configuration for the IF8

Thanks
 
There is no reason to have Integer mode.
Delete the module and reinsert it back as Float Data- Single Ended.
In Float mode you will see scaling parameters under configuration tab.
 

Similar Topics

Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
Replies
4
Views
1,201
Hello, Currently my IF8 is set as 1756-IF8/B Revision 2.011 and my PLC only register as 1.011 which I unable to get the data from the sensor...
Replies
7
Views
1,450
Hi, I'm new here and very much a beginner. I had a question about this AB 1756-IF8 Analog card and how to correctly wire it. I looked in the...
Replies
15
Views
3,872
Can you wire a 1756IF8 analog input card for passive and active instruments at the same time or do they have to be separated. Such as wire 1 card...
Replies
11
Views
4,980
Hello! I am trying to wrap my head around how to wire a 4-20mA sensor to my AB 1756 ControlLogix IF8 Analog Input card. Could someone educate me...
Replies
3
Views
3,759
Back
Top Bottom