1756-ENBT IP Config in RSLogix

kdcui

Lifetime Supporting Member
Join Date
Dec 2007
Location
USA
Posts
386
I was just wondering what the difference between the IP setup on the General Tab and the Port Configuration is.

We have a processor that was a copy and paste of another, however the IP in the General Tab was never changed. However the Port Config is setup with the correct address (it is different than what is in the General tab).

What is the difference between the configs, and when would the processor look at one over the other?

Thanks.
 
The IP address in the General tab is what will set the IP address of the module during a download. The Port Configuration is used to change the IP address when you are ONLINE with the card.
 
Gotcha. Just so I have this straight, if the two tabs are different there should be no conflicts only as long as you don't re-download with the incorrect IP (assuming the IP in the General Tab is the undesirable configuration)?
 

Similar Topics

Hi guys. I'm working on a DH+ system that has RSView32 , PV550 and a PLC5 connected to it. I am adding a ML1400 that messages through Trio...
Replies
5
Views
2,947
please using the usb can i assign any ip address that i want ?
Replies
4
Views
151
Hi, I want to exchange data between two L55 PLCs using ENBT PLC1 is the main PLC and consist of 1756- CNB, L55 CPU and ENBT. Five remote I/O racks...
Replies
7
Views
1,028
Hey guys, I'm not super familiar with Cnet, so I'd like some insight from people with more ControlNet experience than I. We have a controllogix...
Replies
4
Views
892
I am looking into an ethernet drive network system using a Logix5000 system Version 20 and noticed that on the general tab of the properties of...
Replies
1
Views
1,134
Back
Top Bottom