Can someone please help? I want to control the speed of a AB PowerFlex 4 AC drive with a AB ML1100, using a 4 - 20mA output signal. My problem is that I need to invert the output signal from the PLC, so that when the signal is 4mA the drive speed must run at a 100% of the rated speed and 20mA the drive must slow down. Apparently the drive's input signal can't be inverted. Thanks
:confused:
 
Not sure if I understand you corretly. What I think you are saying is that you want to Run a Motor faster via a analog output signal. The speed is based on the level of a analog input signal. The low the input the faster the motor is supposed to run.

Is this what you are trying to do?
 
Can someone please help? I want to control the speed of a AB PowerFlex 4 AC drive with a AB ML1100, using a 4 - 20mA output signal. My problem is that I need to invert the output signal from the PLC, so that when the signal is 4mA the drive speed must run at a 100% of the rated speed and 20mA the drive must slow down. Apparently the drive's input signal can't be inverted. Thanks
:confused:
What you have to do is to use an SCP instruction like this:
input: min=o max=100 ( may be you have different values)
output: max 4 mA, min 20 mA ( may be different valuees, PID etc), then move this data to your 4-20 mA output card.
 
I do have 2 motors. I am monitoring the current on motor A, convert it into a 4 -20mA analog input signal into the PLC. Motor B is controlled via the PLC analog output signal into the VSD. As soon as motor A's current is high, the output analog signal to the VSD must drop to ex. 4mA to slow motor B down. If I use the normal PID, SCL, SCP functions the analog input signal to motor B VSD will also go up linear. I have never used the PID function, so I am not sure which function will work the best.
 
Maybe you could use the SUB(tract) instruction to invert. If you subtract the actual analog value from the Maximum analog value expected it will invert the values.
Source A = integer value for Max output, Source B = Direct integer value derived from other logic, Output = Inverted integer value.

Example:
SOR SUB N7:0 N7:1 N7:2 EOR
 
Last edited:

Similar Topics

Just asking for clarification here, but from my research all I need is a 500 ohm resistor across the AI and the common? Heres my schematic. I...
Replies
5
Views
2,584
Hardware: Micrologix 1100 & 1762-IF4 Analog Input Module Problem: I have one 4-20mA transmitter hooked up to I1:0, I am monitoring the current...
Replies
12
Views
3,372
I have been handed two 0-5v pressure transducers with a 0-15psi range and need to connect them to the MicroLogix 1100 analog inputs (0-10v) for a...
Replies
3
Views
3,032
I am using the AB ML1100 PLC's analog inputs for set point control of a pump for both automatic pumping down a vacuum tank and pumping up of a...
Replies
1
Views
2,986
Please can anybody recommend a way of measuring a negative voltage (-40 to -60V dc) on the analogue input of an Allen Bradley Micrologix 1100 PLC...
Replies
1
Views
2,848
Back
Top Bottom