Aic+

randy

Supporting Member
Join Date
Apr 2002
Posts
158
I'm trying to communicate with a Micro1200, which was configured with the AIC+. I configure my drive (PIC driver), which I had to use RSLinks Launch Control Panel. When I go the Links I can see the driver but not the PLC. I'm using a 1747-CP3 cable. Is this the right cable?

Thanks

rmonroe
 
Just because there is a AIC+ does not mean the ML1200's port is configured for DH485.

The baud rates have to match RSLinx and your ML1200. The node addresses must be different.

Have you tried the DF1 driver?

Do you have the offline file for your ML1200, if so check it's port configuration.

Is this a one port or two port ML1200?
 
Mickey,

I finaly tried the 1747-UIC (DH-485)and it worked. As for the offline original program it was setup for the AB_PIC-1 driver.

Thanks for your feedback...

rmonroe
 

Similar Topics

Hello, currently I have a micrologix 1200 (1762-L40AWAR )connected to an HMI panelview 600(2711-T6C3L1X) via the 1761-net-aic module, I want to...
Replies
13
Views
1,779
Hello! I'm curious if anyone has used ReeR / Mosaic Safety Controllers and can give a short review on how you liked them? I've never used them...
Replies
2
Views
578
I have the following Items connected for DH-485 per the drawing. SLC 5/03 HMI: Automation Direct EA9-T10CL+13Y19B054 1747-AIC #1: connected...
Replies
10
Views
3,047
Hi all. i need an a advice. I use PV800 -T4T or T7T ( to a replace for an old PV550 ). But I have a problem " create communication with PLC...
Replies
1
Views
1,728
Hi, I have SLC 5/03 with 1747-AIC (DH485) modules. Original HMI was PV550, this HMI was replaced to a PanelView 800 (2711R-T7T), communicating is...
Replies
0
Views
1,240
Back
Top Bottom