Well i successfully completed the Modbus RTU to Ethernet I/P project and now i have a BACNet MS/TP to Ethernet I/P, CompactLogix project. Trane Chiller info to AB PLC. Any suggestions on a gateway to do this?
🍻
 
Are you going to be a BACnet MS/TP server or client? The Red Lion Data Station works great as a server but I have not tried using it as a client to read from another device. The Red Lion Allen-Bradley native tag driver is pretty nice too.
 
Not sure how that works? i would need to read/write data between the Red Lion HMI to the Trane Chiller. Also read/write from PLC to HMI to chiller.
 
Im curios how your communicating with the chillers? I would like to collect data from Trane RTHB chillers and not sure where to start. do i need the TCI Modules?
 
Jeff you need to find out what protocols that trane speaks. A quick call to your rep should tell you.
 

Similar Topics

Good Morning from the "Waist Deep in Snow" Mid Atlantic. I have a question about the 2) options that ProSoft has for Ethernet/IP to BACnet/IP...
Replies
4
Views
4,447
Hi all, I have a customer who wishes to to display some of the information from their refrigeration plant (CompactLogix PLC on Ethernet/IP) on...
Replies
9
Views
1,510
I am trying to get data from a Chiller to an AB PLC or to my SCADA system. The protocol is BACNet/Ethernet, which is a layer2 protocol distinct...
Replies
0
Views
1,053
I am in need of a protocol converter from BACnet to Ethernet IP and vice versa. The Ethernet IP end will be an Omron PLC (probably CJ2M) and the...
Replies
10
Views
9,800
Anyone have success using Ignition 8 and the BACNet driver? We are going to try and read data out of our Carrier Chiller. Carrier tech is...
Replies
0
Views
585
Back
Top Bottom