As requested last Friday, here is a ZIPPED copy of the program from the Micrologic 1000 that came up with the fault as per my post on Friday. Anything anyone can find wrong with it would be greatly appreciated.

Thanks
Fred Johns
 
My best guess here is that rung 12 is the culprit. If C5:2.ACC ever becomes greater than 136 then you will have a math overflow when the MUL instruction in rung 12 executes.


edit: Here is the link back to the original thread http://www.plctalk.net/qanda/showthread.php?t=64721
(this helps keep the discussions related to each other so that future readers can benefit from the archived knowledge on the site).
 
Last edited:
I will have to check and see if the rate/hour can go higher then 32767, but it shouldn't from what I remember. It should be constantly changing to give updated machine rates.
 

Similar Topics

I have a micrologic 1000 that is pas word protected. After a few calls I was able to get the pass word from the (now retired) programmer. It was...
Replies
2
Views
3,447
Dear all, Currently i'm working with micrologic 1400 cpu and Temate G5 Controller. I plan to communicate micrologic with temate using...
Replies
0
Views
399
Hi All, I am looking for Modbus Communication Address register details for Schneider ACB Micrologic 6.E0.. We are trying to communicate with AB...
Replies
0
Views
377
I had a question regarding the Micrologix 1400 AI/AO's. I have a 4-20mA AI wired to an input channel (I:3.0) and I am moving that value to an...
Replies
5
Views
1,069
Hello Ken Roach, Thank you for your quick reply , As informed earlier i want to read P&F Sensor data on Micrologic 1400 series B using MSG...