configuration of transmitter

anwer

Member
Join Date
Feb 2012
Location
riyadh
Posts
1
I want to do configuration of ABB pressure transmitter but transmitter model number is not available in hart 375 communicator. my hart has software2.0.
can you give me idea for configuration.

thanks for help
 
The 375 communicator does 6 to 7 common or generic HART commands for any HART device.

Some of those are
- tag name
- units
- URV
- LRV
- square root or linear

If you need to do more than the 6 or 7 common instructions, then you need to load the DD (Device Descriptor) file for the ABB transmitter.

If there is available memory on the 375, then you load the DD into the 375.

The device manufacturer supplies the DD for any specific model (download it from the manufacturer's web site). I assume Rosemount sells some sort of subscription service for managing DD's on the 375, but I don't have one, so I'm not sure of availability or details.
 

Similar Topics

Hello I have a sensor that I read data with IO-LINK but I don't know how to get my data. I see that I have two modes : Process data Map0 and Map...
Replies
0
Views
47
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
Replies
2
Views
87
Hi All, Has any of you tried to change the IP Gateway of the PLC (of course, essentially of the ENBT card), while in a redundant configuration...
Replies
3
Views
127
Hello, Im building project with 1756-L82ES controller and 1756-IB16S card but i cant find it when trying to add the card to IO configuration...
Replies
3
Views
135
Hi all, This is going to be a long post apologies. I'm also a complete beginner to the world of PLCs. I'm currently working on my first ever...
Replies
10
Views
453
Back
Top Bottom