SLC503 to G306M

John Simmonds

Member
Join Date
Jun 2008
Location
Tennessee
Posts
15
How do I set up comm between Red Lion G306M and SLC503? I've tried using cable CBLAB003 from Channel 0 to RS485 port on G306M - what am I missing? John
 
Hello,

The cable you have is correct. Can you tell me how you have the port configured on the PLC and HMI?

Thanks
Jeremy
 
Hello Jeremy, I've shown the configuration in the attached files. Thanks, John

I see you have the G306M port set to 4wire but it should be 2wire which is the default. Also I would like to see how the device PLC1 is configured as well as each channel configuration in the PLC.

Thanks
Jeremy
 
Thanks both, for your replies. PLC1 is set to SLC but after I changed to 2-wire I could see the data from PLC - trouble is... it's flashing. How can I stop this. Attached file shows settings for PLC1 and text. John
 
Flashing data would indicate that you have a comms error somewhere in your system. The good data flashes to let you know of the problem. Most likely there is a misaligned tag.

Thanks
Jeremy
 

Similar Topics

One of my customers is interested in extracting some data from a machine running on an SLC503 and they really don't want to change the PLC in any...
Replies
5
Views
1,551
what cable and what module do I need to have the powerflex4m drive communication with slc503, I now have 22-scm-232 and 22-RJ45CBL-C20 CABLE, Does...
Replies
3
Views
1,396
Hi, The scenario: The system has been working fine for many years. There is an intermittent issue somewhere. I have yet to look for error...
Replies
2
Views
1,195
It seems like I have asked this before, but I guess I didn’t like the answer ! In RSLogix for a SLC503, I have an exact copy of a program but . ...
Replies
3
Views
1,831
Wow, it's been awhile since I've been on here. But, I'm so glad this forum exists. I know, no one really likes the AB panelview component HMIs...
Replies
9
Views
3,880
Back
Top Bottom