sparkytex
Lifetime Supporting Member
Got called out to check out a problem with an amp read out on the winview HMI for a 150 hp motor. Using AB PLC5 1771 IFE analog input card. When i look under I/O config and pull up that module there is a zero in the data column under ch.16. I got an electrician to hook up a signal generator to validate that the card is still sending data to the PLC and i'm getting nothing. It says on the side of the module that terminal 19 is input 16 on a single ended signal and terminal 20 is module common. He had the signal generator hooked up positive to 19 and negative to 20 and set to source 4-20mA. Is this hooked up incoorectly or is there something else im missing? What does it mean when a data value is highlighted in yellow? also is there a way i can force a data number into the column so i can make sure the operator see's the value in the HMI? thanks again, this day has been a nightmare