I have a bad output module 1746-0A16 ser. C. I have a spare module 1746-0A16 ser. B I would like to use to replace this bad unit. What is the difference between the Ser. B and C and can I make this swap without any issues?
 
you shouldn't have any issues using the B to replace the C ...

but ...

the real question is: WHY is the C "bad" in the first place? ...

suggestion:

tell us more about what you're seeing - and how you're testing - and maybe we can help save you some trouble ...

TIP: these TRIAC types of modules usually don't just "go bad" for no reason ... did it get overloaded - and "pop" an output? ... are you testing its outputs with a meter - and finding that the outputs are all testing ON - even though they should be OFF? ... etc. ...
 
Last edited:
I have one output terminal that is remaining energized and powering a solenoid valve to a Pneumatic pump when the output is off. The pump is remaining on at all times. This has always worked normally in the past and has just recently started. We did have a coil go bad on the solenoid to the pump and I'm thinking it may have damaged the output causing it to remain energized.
 
We did have a coil go bad on the solenoid to the pump and I'm thinking it may have damaged the output causing it to remain energized.

based on that - your conclusions make perfect sense ... sounds like replacing the module is the answer ...
 

Similar Topics

Can somebody tell me if the rung comments and instruction comments are stored in the slc 500 controller or are they stored on you hard drive
Replies
10
Views
2,967
I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
Replies
48
Views
1,023
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
Replies
9
Views
798
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
Replies
16
Views
1,391
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
Replies
7
Views
572
Back
Top Bottom