I have two 1734-AENTR/B remote I/O racks attached to a 1769-L33ERM processor.


Both racks are communicating; the inputs update in the PLC as the sensor states change.


The problem is that when output bit states change in the PLC, the states of the output bits on the rack do not change.


However, if I force any bit on or off, all of the output bits on that rack are updated.


So I know that the output bits on the rack are accessible to the PLC.


It seems that the PLC is not sending output data under normal conditions—only in the event of a bit force.

Any suggestions on how to fix this?
 
That is a weird one. The first thing that comes to mind is conflicting logic. One rung turns the output on but another rung is tuning it off. A force would override the program and just turn the output on no matter what the program is telling it. I have seen this several times with my own programs. Do a cross reference and see if you can find other places where the output or bit is used and go from there.
 
Program validates ok; the bits in question do not have multiple destructive writes.

It is not just one or two bits that do not update as expected. No output bit on either rack updates during the normal scan.

I'm requesting manual operations from the HMI. Requests that are accepted in the rung logic result in OTE to a local tag. At the end of the application program, all local tag bits are copied to the output module Data arrays.

The Data array bits are updating correctly in the processor. But the LEDs on the remote racks do not change.

When I force any single bit on, ALL outputs for that rack are updated to match the values already showing in the PLC.
 
Solved, with help from Rockwell Tech support. In the task that writes to the outputs, in the Properties dialog under the Configuration tab, be sure that "Disable Automatic Output Processing To Reduce Task Overhead" is not checked.
 

Similar Topics

Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
95
Hello. Was just curious, if it is possible to load an image from an SD card on to a Compactlogix PLC that came straight out of the box brand new...
Replies
4
Views
545
I'm working on troubleshooting a PLC for a piece of manufacturing equipment. The issue I'm trying to resolve is an open wire fault not getting...
Replies
2
Views
531
Hi all, this is my first post and appreciate your advise in advance. I have a job to migrate a system form Mitsubishi FX5U to AB...
Replies
2
Views
841
Hello Everyone, A very important question: We are having trouble receiving analog output cards (5069-OF4) for our CompactLogix PLC racks. I am...
Replies
12
Views
3,188
Back
Top Bottom