Panelview Plus 1500 with Factory Talk 6.0

jasil

Member
Join Date
Jun 2012
Location
Building
Posts
48
We have a PV 1500 that communicates with 13 PLC from PLC 5 to Contollogix. Running 6.0 because corporate doesn't want to upgrade :(

We just upgraded some PLC 5's to L72 Processors running RsLogix 20.1

When we test the panel view app in Factorytalk on the laptop every screen works fine. When we run on the Panel view nothing from those new PLCs populates all errors.

My fear is I need to be using FT 7.0, but nothing else makes sense. Runs fine on the laptop not fine on the PV suggestions??
 
We get a rslinxng.exe needs to shutdown due to a major error. Again every screen works and changes except the 2 on L72 processors
 
Yes......we went to config and even verified the setting are the same in the pc vs the panel view.

Just don't know if it's Factorytalk or a Linx issue. We do get a rslinxng.exe fault when the app loads , so ??
 
Are you testing a single screen or testing using the running man?
I know I recently had to upgrade RSLinx Enterprise for a new compactLogix but I couldn't see it on the computer.
 
Test using the running man as it uses the run-time communication from my understanding.
 
Yes it works with the running man and replace comms is checked.

Someone has a copy FT 8.0 we are going to put that on there and see what happens.
 
Bob O said:
According to this PDF page 6 you need RSLinx Enterprise 5.50 for V20 software...

Correct Bob O, but it's the v20 "hardware" that needs the software support, more so than the "V20 software", but I know what you meant.

To add support for v20 Controllers:
For the PC you can upgrade to RSLinx Enterprise v5.50 minimum.
For the PVP terminal you can flash the firmware to v5.10.08 minimum.

See here...

490905 - RSLinx Enterprise: Support for RSLogix 5000 version 20 controllers
Access Level: Everyone

If you cannot do either or both of the above, then you can patch RSLinx Enterprise (also linked in the above technote)...

493707 - RSLinx Enterprise 5.30.00 (CPR9 SR3) Patch: Need support Logix V20 controllers
Access Level: Everyone

Regards,
George
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
146
Hi there, Maybe I am overthinking this issue, but here is what I have going on. I have a program running for a water valve on a DI system. We...
Replies
4
Views
501
Hi guys. Currently working on a project that requires a Panelview Plus 1500 to read a CSV File (recipe) from a network drive. The issue I have...
Replies
1
Views
1,072
Hi, guys, how’s going? I added one “Trend Object” on screen A in PanelView Plus 1500. Then configured “Refresh Rate”, “Buffer” ……and set up...
Replies
2
Views
1,951
Good morning, I am onsite at a customer. They have a panel view plus 1500 that does not light up. The screen is always black. I am not very...
Replies
16
Views
5,665
Back
Top Bottom