I am trying to use a NET-ENI to connect to a Micrologix 1500 with Ethernet. I am not trying to use email or anything tricky. I just want to go online with the programming software. RSWho in RSLinx Lite tells me the device type is unrecognized. This is supposed to be easy. Any ideas?
This is all of the configuration data:
Cable from Micrologix to ENI is 1761-CBL-AM00 Ser A
Laptop is connected to the ENI with a crossover cable.
The PLC is Micrologix 1500 (1764-28BXB Ser A Rev A)
Channel 0 is set for DF1 Full Duplex
Baud = 19200
Parity = NONE
Source ID = 1
Control Line = No Handshaking
Error Detection = CRC
Embeded Responses = Auto Detect
ACK timeout (x20ms) = 50
NAK retries = 3
ENQ retries
Duplicate Packet Detect is checked
The ENI is 1761-NET-ENI Ser B FRN 2.00
232 Baud rate is set to Auto
The IP Address is 192.168.000.023
The subnet mask is 255.255.255.000
Gateway and both security masks are all 0
Message routing is all 0
Nothing is set on the email tab
The laptop is Windows 98
Static IP address is 192.168.0.21
Subnet mask is 255.255.255.0
WINS is disabled
no gateway
DNS is disabled
RSLinx lite is version 2.41.00
Ethernet driver
Station 0 host name is 192.168.000.023
This is all of the configuration data:
Cable from Micrologix to ENI is 1761-CBL-AM00 Ser A
Laptop is connected to the ENI with a crossover cable.
The PLC is Micrologix 1500 (1764-28BXB Ser A Rev A)
Channel 0 is set for DF1 Full Duplex
Baud = 19200
Parity = NONE
Source ID = 1
Control Line = No Handshaking
Error Detection = CRC
Embeded Responses = Auto Detect
ACK timeout (x20ms) = 50
NAK retries = 3
ENQ retries
Duplicate Packet Detect is checked
The ENI is 1761-NET-ENI Ser B FRN 2.00
232 Baud rate is set to Auto
The IP Address is 192.168.000.023
The subnet mask is 255.255.255.000
Gateway and both security masks are all 0
Message routing is all 0
Nothing is set on the email tab
The laptop is Windows 98
Static IP address is 192.168.0.21
Subnet mask is 255.255.255.0
WINS is disabled
no gateway
DNS is disabled
RSLinx lite is version 2.41.00
Ethernet driver
Station 0 host name is 192.168.000.023