joeparrish
Member
United States

joeparrish is offline
 
Join Date: Nov 2007
Location: owensboro ky
Posts: 160
ac motor wire size

I was wondering if anyone knows the wire size for a 3 phase 200hp motor for an air comp

the uglys book only goes to 150hp motors

also where would I find this info
  Reply With Quote
Old October 1st, 2009, 02:54 PM   #2
joeparrish
Member
United States

joeparrish is offline
 
Join Date: Nov 2007
Location: owensboro ky
Posts: 160
it says max draw is 280 amps
  Reply With Quote
Old October 1st, 2009, 03:06 PM   #3
leitmotif
Member
United States

leitmotif is offline
 
Join Date: Nov 2004
Location: Seattle Wa. USA
Posts: 3,680
The most correct would be NEC. Yes they run you thru several tables to get to the wire size. I would tend to add one wire size just to make sure and I for sure would do a voltage drop calc if a long ways from source ie main distribution not the disconnect.

Dan Bentler
  Reply With Quote
Old October 1st, 2009, 03:39 PM   #4
OZEE
Member
United States

OZEE is offline
 
Join Date: Mar 2006
Location: Kansas
Posts: 1,695
My cheat sheet shows 350MCM, but that could need adjusted up depending on your deratings.
__________________
"I wonder how people did this before the days of PLCs?" If people would take the time to learn how a simple relay control circuit works..... [Helliana]
  Reply With Quote
Old October 1st, 2009, 03:51 PM   #5
robertmee
Member
United States

robertmee is offline
 
robertmee's Avatar
 
Join Date: Feb 2008
Location: NC
Posts: 1,428
I agree with OZEE, 350MCM, however, as he noted, depends on other derating factors such as:

Ambient temperature
How many additional conductors in raceway/conduit? (are you doing point to point from motor distribution to the motor or are you sharing larger conduit/raceway with other conductors?)

EDIT: Of course assuming standard type insulation and copper wiring.
  Reply With Quote
Old October 1st, 2009, 04:50 PM   #6
darkesha
Member
Canada

darkesha is offline
 
Join Date: Nov 2007
Location: Calgary
Posts: 99
Quote:
Originally Posted by joeparrish View Post
I was wondering if anyone knows the wire size for a 3 phase 200hp motor for an air comp

the uglys book only goes to 150hp motors

also where would I find this info

What is FLA and Voltage, 480, 575 V?

At 460V and 240 A [fla] table says 250MCM
or 575V and 192 A [fla] table says 000
Thats according to CEC and no derrating.
  Reply With Quote
Old October 1st, 2009, 05:14 PM   #7
ndzied1
Lifetime Supporting Member
United States

ndzied1 is offline
 
ndzied1's Avatar
 
Join Date: Aug 2002
Location: Chicago, Illinois
Posts: 2,381
My "Cheat" slide from Eaton says for a 200HP at 575V, 3PH, 60Hz you'd go with a minimum of 250MCM but do the calcs for other effects as others have recommended.
__________________
nOrM
======================
nOrM=Norman Dziedzic Jr.
"I decry the current tendency to seek patents on algorithms. There are better ways to earn a living than to prevent other people from making use of one's contributions to computer science." Donald Knuth
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Panel Builder 32 Array Size The Plc Kid LIVE PLC Questions And Answers 3 August 27th, 2009 05:48 PM
" do not care for AC connection " is this statement correct ?? magdyfayad LIVE PLC Questions And Answers 26 October 3rd, 2008 10:52 AM
AC Drives - AC Input current, DC Bus current swhite65 LIVE PLC Questions And Answers 10 June 25th, 2007 04:05 AM
Changing AC to DC motor ettore LIVE PLC Questions And Answers 3 June 7th, 2005 09:55 AM
SErvo Vs AC motors haythame78 LIVE PLC Questions And Answers 8 March 10th, 2005 11:43 AM