ac motor wire size
joeparrish
Nov 2007
owensboro ky
161
I was wondering if anyone knows the wire size for a 3 phase 200hp motor for an air comp
the uglys book only goes to 150hp motors
also where would I find this info
The most correct would be NEC. Yes they run you thru several tables to get to the wire size. I would tend to add one wire size just to make sure and I for sure would do a voltage drop calc if a long ways from source ie main distribution not the disconnect.
Dan Bentler
I agree with OZEE, 350MCM, however, as he noted, depends on other derating factors such as:
Ambient temperature
How many additional conductors in raceway/conduit? (are you doing point to point from motor distribution to the motor or are you sharing larger conduit/raceway with other conductors?)
EDIT: Of course assuming standard type insulation and copper wiring.
What is FLA and Voltage, 480, 575 V?
At 460V and 240 A [fla] table says 250MCM
or 575V and 192 A [fla] table says 000
Thats according to CEC and no derrating.
My "Cheat" slide from Eaton says for a 200HP at 575V, 3PH, 60Hz you'd go with a minimum of 250MCM but do the calcs for other effects as others have recommended.
Hi everyone ! A multiconductor wire 4x2,5mm2 would be ok ? Normally a 10hp - 400V motor would pull 16-17A A 4x2,5mm2 wire could carry around...
1,859
Good morning, Curious what the function is of this piece of steel pipe that a motor wire run through. The same thing is installed in the encoder...
2,709
Hi everyone, I am part of a senior design group that is building a dynonameter to test shocks. We are ordering parts tomorrow morning and so I...
17
10,105
Sorry, Not PLC related, but there is a lot of kowledge here. Over the weekend a mechanic had to replace a burnt motor, the replacement was a 12...
2,615
Hi all, I have an actuator which I need to control with an AB PLC. Its a 5 core actuator which a motor and limit switch. To extend the arm I...
53
15,918