Correct method OF Cold JUNCTION compensation
jose7771
Jan 2005
42
Hello frnds
Is This the correct method of cold junction compenation
Vnet =VhOT -Vcold(ref)
therefore VhOT =Vnet+Vcold(ref)
so V ref at 30 deg celsius say X mv
watever O/p V R gettting v have to add X mv for cold junction compenation
in our PLC/DCS
Is IT RIGHT ?
REGRADS
jos
cold junction compensation
Dear Mr.Jose,
We have to consider the difference between the Actual temperature and Reference temperature (taken for calibration) of cold junction. However these are now being taken care in the AI cards.
RT
Electronic devices add the CJC to the thermocouple reading, so the formula is
temperature = thermocouple reading + CJC value
where CJC is the difference between the AI terminal block temperature and the freezing point of water (0°C).
Example:
The temperature being measured is 121°C
T/C hot end is 121°C
T/C cold end at AI input terminal block is 35°C.
The gradient across the thermocouple will be 121-35° = 86°C in equivalent millivolts, depending on the type of T/C.
The cold junction circuit measures the temperature of the terminal block, 35°C in this case. That value is added to the temperature represented by the millivolt value, 86°C, to get the hot end temperature value, 121°C.
121°C = 86°C + 35°C
Dan
Daft question coming up...When I want to modify a value, what's the best/correct way to do this? At the moment, I am entering the value (e.g...
434
Good day. I encountered a problem when calibrating a channel on the IF16H module. The module is located in the local backplane along with the...
739
I have some programs that i received from 1 of our programmers whos installing a new machine in our plant. He added them to a external hard drive...
1,357
Hi, At the moment, If the user fails to provide a valid username/password, the image attached appears "Invalid password or user name. Logon has...
1,573
Hi, In a Direct On Line circuit for CW and CCW operation of a 3 phase motor, what is the right way to interlock the contactors. 1) Use a NC...
1,534