Hello,

I had a thread about downloading the application file to panelview 300 without Panel builder 32 and some kind people here helped me out with that. I thank all of them for the help.

Now the real issue with the installation is that the application in the panelview gets erased automatically. We have 4 panelview 300 micros installed on 4 machines (air dryers). We have faced 4 cases of the application file being erased from the panelview without anybody doing it.

I would like to know if bad earthing can be a problem here or what is the nominal earth current allowable for Panelview. Or if anybody has faced such issues with any AB panelviews and if so what was the remedy.

I've tried searching the figures on AB site but was unable to get a decent result.

Any help will be highly appreciated.
 
I would think that power quality might be a factor. We were using the PV300 micro in several locations, some of which are a bit hostile, and they died frequently. Ours would come up blank, with only a backlight, or the display would be garbled.

We replaced one of them in the worst environment with a Red Lion G304K. So far it has been running for over a month without any problems. It is a much more capable device, less expensive, and the programming software is free. The panel cut out for the G304K is slightly larger than the 300 Micro. In my opinion it is a great replacement. It will talk DF1, DH485, and many other non-AB protocols. So, I can't think of anything the 300 Micro can do that the G304K can't do faster and better.

Paul
 
Last edited:

Similar Topics

Is this the clock battery flat? Does anyone know how to remove the back of the PV 300 micro. Is it possible to replace this battery. AB says it's...
Replies
2
Views
1,191
I have an opportunity to get some more experience replacing an old Panelview 300 Micro. I'd like to hear any advice you have about it. I suspect...
Replies
12
Views
3,324
I lost the manual for this machine built in 2003 and need to put it back together. I have the Micrologix 1200 and PanelView 300 Micro programs...
Replies
4
Views
1,789
I am tying to download application software to a fresh out of the box PV 300 Micro. The first hitch is a prompt that I am running v4.1xx RSLinx...
Replies
2
Views
1,153
I went on a service call yesterday for a Micrologix 1500. An output wasn't activating and they wanted to know what was hanging it up. It was a...
Replies
10
Views
2,823
Back
Top Bottom