Question Motor start timer after losing power

Hello
I have two 480v motors that has remote start capability.
When the remote start button is pressed the 1st motor starts in 15 seconds.
When the remote start button is pressed on the 2nd motor it starts in 30 seconds. I do this so they are not both started at the same time.

The issue that I’m having is if we lose the 480v power or blow a fuse, but
keep 110v power in the PLC panel because of a ups keeps it up. Then what happens is since the start Command was enabled on both motors before the power was lost, then they will both start after the 480v power is restored.

Is there any Logix that I could program into the PLC
that would prevent both motors from starting after
480v Power is restored? If this is possible could you
post examples?

I have a Allen Bradley 1769-L32E controller
I monitor the motor amps and vibration currently
In the plc. Could I use any of these?

I appreciate the help

Last edited by Ones_Zeros; July 12th, 2019 at 06:11 PM.
  Reply With Quote
Old July 12th, 2019, 06:22 PM   #2
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,535
Since you said you are monitoring the amps (assuming you mean all 3 phases),
you could program a latch bit for motor 1 and 2 - motor1 on / motor2 on.
in your logic I would say if the output is on and motor1 latch bit is on and any one of the phase currents for motor 1 drops below 1 amp (you didn't sat what hp so you could make it 5 amps if it is a 30 hp motor), then set a motor 1 power loss bit to turn off the motor 1 logic. only when the power is restored and you hit the start button for motor 1 will the system start the timer.

it's been a long and trying to go home.
just an idea I had and I hope this helps.

james
  Reply With Quote
Old July 12th, 2019, 09:51 PM   #3
willxfmr
Lifetime Supporting Member
United States

willxfmr is offline
 
willxfmr's Avatar
 
Join Date: Nov 2013
Location: Wisconsin
Posts: 379
If the UPS is fed by a transformer off the 480, then you could use a simple cube relay on the line side of the power feeding the UPS. Line power energizes the relay, and a set of NO contacts go to the PLC to signal power loss. From there, you can use the input any way you choose. There are a bunch of power indicators available, but cube relays are cheap to install, and easy to replace.

Bubba.
__________________
Now will come the nay-sayers with all the reasons why you shouldn't do this. Some of them are teachers, and some of us are doers. Besides, you have got to let the smoke out of this equipment every now and then, or it starts to clog up the chimney.
~Lancie1

Last edited by willxfmr; July 12th, 2019 at 09:51 PM. Reason: Proof read... then post. Not the other way around silly.
  Reply With Quote
Old July 12th, 2019, 11:04 PM   #4
MasterBlaster
Lifetime Supporting Member
United States

MasterBlaster is offline
 
Join Date: Aug 2005
Location: Solano County, CA
Posts: 200
What Willxfmr said. Years of similar issues taught me to ALWAYS have a “Commercial Power Available” bit, and if the pump station was also generator-backed, there was a “Generator Power Avaialble” bit. With those, the rest is easy.
  Reply With Quote
Old July 12th, 2019, 11:42 PM   #5
EICS
Member
Australia

EICS is online now
 
EICS's Avatar
 
Join Date: Dec 2008
Location: Melbourne
Posts: 195
as willxfmr said


+1
  Reply With Quote
Old July 13th, 2019, 04:15 AM   #6
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 772
Quote:
Originally Posted by willxfmr View Post
If the UPS is fed by a transformer off the 480, then you could use a simple cube relay on the line side of the power feeding the UPS. Line power energizes the relay, and a set of NO contacts go to the PLC to signal power loss. From there, you can use the input any way you choose. There are a bunch of power indicators available, but cube relays are cheap to install, and easy to replace.

Bubba.
This. Keep it simple.
  Reply With Quote
Old July 13th, 2019, 04:49 AM   #7
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 1,028
UPS's usually have a set of dry contacts on them, too.
  Reply With Quote
Old July 13th, 2019, 08:17 AM   #8
Ones_Zeros
Member
United States

Ones_Zeros is offline
 
Join Date: Feb 2014
Location: at work
Posts: 240
Thanks a lot guys
I appreciate the help
You have been very helpful

Thanks!
  Reply With Quote
Old July 13th, 2019, 09:03 AM   #9
Ones_Zeros
Member
United States

Ones_Zeros is offline
 
Join Date: Feb 2014
Location: at work
Posts: 240
would you guys recommend any specific cube relay for this type application?

thanks again
  Reply With Quote
Old July 17th, 2019, 10:47 AM   #10
Nethop
Member
Canada

Nethop is offline
 
Join Date: Dec 2012
Location: BC
Posts: 18
http://time-mark.com/shop/3-phase-monitors/257b/
  Reply With Quote
Old July 17th, 2019, 11:49 AM   #11
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 438
With the motor amps you can detect if the motors are running, when they stop for any reason then signal the fault and reset the timers, the operator will have to press the button again to start.
__________________
Suppanel HMI
  Reply With Quote
Old July 22nd, 2019, 01:30 PM   #12
shooter
Member
Netherlands

shooter is offline
 
shooter's Avatar
 
Join Date: Sep 2002
Location: duketown
Posts: 2,708
indeed check if running signal if not just rest the timers for any motor.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
  Reply With Quote
Old July 22nd, 2019, 08:40 PM   #13
Ones_Zeros
Member
United States

Ones_Zeros is offline
 
Join Date: Feb 2014
Location: at work
Posts: 240
Since Im currently monitoring amps. How would be the best
Method to program this?

What I was thinking was if the amps go to zero
then de-energized a memory bit and start a timer to unlatch a bit to
Prevent startup.

Then when the 480v is restored the operator
would have to Press button to restart motor which would also unlatch
The bit that was latched

If Im off here please help me simplify this

Thanks
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Automated Parking System Using OMRON PLC and HMI kannan_kathiresan LIVE PLC Questions And Answers 196 October 13th, 2014 05:35 AM
AB SLC-500 Beginner Questions 2k1Toaster LIVE PLC Questions And Answers 37 April 15th, 2014 05:05 PM
2 24VDC power supplies cskaggs2 LIVE PLC Questions And Answers 5 September 15th, 2010 11:24 PM
what are the advantages for three phase power supply than single phase power supply ? magdyfayad LIVE PLC Questions And Answers 6 October 28th, 2008 02:42 PM
Analogue Inputs - Sink, Source, Help! Yabadabadoo LIVE PLC Questions And Answers 14 January 26th, 2005 12:48 PM


All times are GMT -5. The time now is 02:47 AM.


.