PanelView Plus 400 - Problem displaying alarms in an Alarm Status List.
scott_8812
Apr 2014
Brisbane
I am using a Micrologix 1400 talking to a Panelview Plus 400 with firmware 5.10 and using FactoryTalk View Studio - Machine Edition.
When one alarm is triggered, it is displayed at the top of the list, all good. Then when a second alarm is triggered, is moves the first alarm down but only displays a blank space at the top of the list. If a third alarm is triggered, it pushes the first alarm down again and displays two blank spaces at the top of the list.
If I navigate away from the Alarm screen and then back to it, the third alarm will then be displayed, and the other two previous alarms are hiding underneath it. If I clear the alarm that is showing, the next active one appears in its place rather then being listed.
I believe the problem is within the setup of the Alarm Status List. I have it set to display Active Alarms.
Any ideas or suggestions appreciated.
Hello . Info: Panelview plus 400 2711P-K4M20D Compactlogix 1769-l32E i make a program in RSlogix 5000 and Factorytalk view for...
1,804
Hello again, We are working on a system that we developed and had been working fine for years. Recently, the customer decided that they needed to...
1,710
Hello, I have a CompactLogix with Ehternet port and would like to know if a PanelView Plus 400 (2711P-KM20D SerB) will work with it, please? I do...
1,663
Hi there, I seem to be having some issues interfacing a Mircologix 1400 and a Panelview plus 1000. All communication is done over ethernet...
2,377
Hi. I am working with a PanelView Plus 6 600 and noticed that the resolution size is the same as the PanelView Plus 6 400. I'm a little...
2,817