![]() ![]() ![]() ![]() This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc. |
||
![]() |
![]() |
#1 |
Member
![]() ![]() Join Date: Oct 2013
Location: Northampton
Posts: 119
|
fan and air mixer combined PIDE (Guardlogix) with PowerFlex drive
Hi All
I'd be interested to hear approaches hear on what options you might consider for setting up of the loop control. I'll describe the setup. We have a test cell that has a basic air 'conditioning' setup. There is a fan with a fairly big, inefficient motor run from a PowerFlex 525. The duct work has vents from the fan into the front of the cell and a vent pulling it back out from the rear of the cell back to the fan. We also have a mixing arrangement where there is a full intake and full exhaust externally of the building. As well as controlling the fan speed via the Powerflex (min 10Hz to max 50Hz) we have a paddle in the mixing arrangement controlled by an electro-pneumatic actuator that can block the paths to ensure that the cell is fully exhausting to the outside work and thus pulling completely fresh in from outside, or the paddle can be blocking off the outside connections to fully recirculate the air in the cell and with the benefit of the inefficient motor provide a pretty dirty, but effective cell heating capability. Obviously the paddle can opertate anywhere between these two conditions and is controlled with a 4-20mA from the PLC (the PowerFlex will be speed controlled via EtherNet connection between the PLC and PowerFlex). In 99% of occasions we want to keep the fan speed running as slow as posible for two reasons, more economic from a power point of view and much, much quieter from a noise point of view. Thus we would tend to rely of modulating the mixing paddle accordingly. However, if we were dumping a lot of heat into the room the paddle may go to fully exhausting and then we still need to then increase the speed of the fan. However as soon as we do that then the paddle may act and start modulating. I'd be interested to hear about how you guys might set this up. A secondary means of operation is the option to fully override the control and do max fan speed with full exhaust to evacuate the cell of any fumes in the case of a failure with then potentially shutting off the fan and moving the paddle to fully cell recirc to prevent providing oxygen in the case of a fire. These cases need to be fully defined by the appropriate risk assessment and H&S desing reviews. Any thoughts on how you might link up these two PIDE loops for the fan motor speed and the paddle position would be gratefully received. thanks, -BG- |
![]() |
![]() |
#2 |
Member
|
While the following thread does not exactly match the application described, it may offer some ideas to help develop a control strategy.
Sanity Check - Process Control
__________________
"The greatest enemy of knowledge is not ignorance, it is the illusion of knowledge." -Stephen Hawking |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Oct 2013
Location: Northampton
Posts: 119
|
Many thanks, I did have a quick lread through and there is some interesting stuff in there. It seems the images are not hosted correctly anymore, not that it matters too much.
I'm inclined at the minute to run the mixer valve paddle on a much faster loop than the fan motor speed. It would need to be at least as fast to see the PV change on the fast loop and act before the motor speed loop reacted to work I guess. |
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Oct 2013
Location: Northampton
Posts: 119
|
Hi all. Just following up on this I thought that i'd add a bit of an image to supplement the description in my first post.
![]() I am showing two seperate PIDE instructions that are working off the same process variable (PV) from the cell RTD and the same setpoint (a temperature set by the operator). The fan has to run at a minimum of 10hz to keep the motor happy, but I would like the mixer paddle to control through its position (vertical is max cooling as full intake/exhaust to the outside world, horizontal is max heating through full recirculation and heat input from the inefficient fan motor). The air mixer paddle should be the predominant control and only when it gets close to full intake/ehaust at the vertical position (so CV =100%) should the fan motor PIDE 2 begin to function and look to ramp the speed up from 10Hz up to its max of 50Hz. Equally, when the cell gets too cool it should bias the opposite way to do everything to reduce the fan speed down to 10Hz before really looking to contorl through rotating the air mixing paddle towards the horizontal (CV=0%). |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Nov 2016
Location: Fields of corn
Posts: 1,815
|
Wouldn't the fan have the inverse control variable of the mixer paddle?
" The fan has to run at a minimum of 10hz to keep the motor happy, but I would like the mixer paddle to control through its position (vertical is max cooling as full intake/exhaust to the outside world, horizontal is max heating through full recirculation and heat input from the inefficient fan motor)." There's some added math for scaling, but if you command your mixer to 30% and fan to 70%, would it do what you're after? |
![]() |
![]() |
#6 |
Lifetime Supporting Member
|
Is external air always cooler than the temperature setpoint? I would think it would have to be else cooling would not be possible.
What are the external loads i.e. what else is cooling or heating the sensor? When the paddle is closed (horizontal in the image; 0%), will the fan ever need to be increased above 10Hz to heat (I think this is what @cardosocea is getting at)? Either way, I think a single PID with a split range output may be called for:
Also transitions at N% and M% might get messy, so perhaps some overlap - or gap (i.e. deadband) - at those transitions makes sense. Noise in the PV may cause problems here, requiring filtering. I suspect this going to be a slow process; an Integral-only control system might work. There may be some deadtime on the intake air, but it may be small compared to the system time constant. Varying intake air temperature may make the tuning a challenge; perhaps M and N could be a function of outside air temperature. Last edited by drbitboy; April 8th, 2021 at 09:25 AM. |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Sanity CHeck - Process Control | ASF | LIVE PLC Questions And Answers | 20 | November 28th, 2018 10:06 PM |
DOL chnaged to PowerFlex 525 Issue | lanester | LIVE PLC Questions And Answers | 3 | March 28th, 2017 01:25 PM |
PowerFlex 400 PID Loop for DryCooler Fan / Temperature / Modbus | alexhk | LIVE PLC Questions And Answers | 1 | December 22nd, 2013 09:36 AM |
PID control - air pressure - Devicenet -160Bulletin Analog drive | Daggi | LIVE PLC Questions And Answers | 0 | April 23rd, 2003 11:15 AM |