Conditional Block End (BEC) by S7-1500 in TIA Portal
spandy16
Dec 2012
Germany
58
I had migrated my software from S7-300 controller to S7-1500 controller in TIA Portal. Afterwards I got an error in one FB during compilation, saying "RLO is not initialized". The code was as follows,
NW1: condition 1, condition 2 then JMP: END
NW X: END: NOP 0
BEC
My question, is it possible that I use a RET instruction directly in the first RUNG with the conditions and remove the BEC code?
NW X: END: NOP 0
BEC
Is there any code after the BEC, if not use BEU
That does sound logical but why was the jump there in the first place? It could have been written Condition 1, condition 2 etc BEC. In S7 classic, the JP instruction does not set the status of RLO so I guess that the same applies to TIA. If the original jump instruction was JC then RLO is set to 1 when JC is executed so you can write:
Code:
A I xxx
O M yyy
JC M001
S M zzz
JU END
M001: R M zzz
END: NOP 0
Nick
The JMP was there because the next Logic instructions could be executed if the JMP condition was not satisfied. And the BEC command is in the last Network of the FB.
Is it possible that I use
END: SET
BEC
Code:
A I xxx
O M yyy
JC M001
S M zzz
JU END
M001: R M zzz
END: NOP 0
Nick
If the 1500 works like the 300/400 (which I don't know ...yet), it is good practice to end all blocks with
SET
SAVE
This sets the ENO (and BR) to TRUE and you can link other blocks when used in LAD(KOP) and FBD(FUP).
Kalle
My code would have looked like this
NW1: condition 1, condition 2 then BEC
BE
If its the last bit of code, why jump down to BE
SET
SAVE
Kalle
In all my years of programming S7, I never once did SET, SAVE at the end of a Function. I never used it to continue code outside the block, which I believe is the only time you would do that.
Yes.
If you call the FB/FC in LAD you can continue the rung from the ENO. This can also be convenient in FBD and even in CFC.
Kalle
I had migrated my software from S7-300 controller to S7-1500 controller in TIA Portal. Afterwards I got an error in one FB during compilation...
1,595
Hi I'm trying to read a block of 10 values from a plc, based upon time or a signal from the plc. I have managed to setup the links and have used...