russrmartin
Member
Hi people, I have another scenario and I'm looking for answers. The situation is an extruder and die that has electrical heater control done with a PLC5. The PID loops for these heaters were referred to by RTD's. Recently, one of our techs replaced the RTD's with thermocouples. He failed to startup and checkout the machine, so I am left with this. We have a bit (b3 example)that is labeled as a "Zone 1 alarm RTD open heating. This bit is the output to a rung that looks like this. A normally open fault enable bit, which leads to an N17:0/0. This N17:0/0 is labeled as "zone 1 underrange". In parallel with that bit is another bit, normally open N17:0/8. This bit has no description. After these two integer bits in parallel with each other comes the output. What I am having trouble comprehending is this. I search the N17:0/8 or 0/0, and the only place is shows up is in this rung. WHen viewed in binary under the data table, I can see that n17:0/8 is set to 1, and 0/0 is set to 0. I know that this number is being written in there somehow, because I cannot simply force them to the opposite states. When I change the value, they are changed back again. I see where various RTD's are wired to inputs that are labeled as N17 words, but the prints show nothing in the column where the word N17:0 would be. Therefore, I am perplexed as to where this information is coming from. My understanding is that with the old RTD's we used this word, and now with thermocouples we will not need them. But before I take them out, I'd like to have a better understanding why they were there. Any input will help, sometimes if I jog my brain I can figure things out, but I have hit a road block. Thanks in advance.
Russ
Russ